Posted: 2021-07-08 12:15 AM
This was originally posted on APC forums on 4/6/2015
i have a APC Web/SNMP Management Card (MB:v4.1.0 PF:v6.2.1 PN:apc_hw05_aos_621.bin AF1:v6.2.1 AN1:apc_hw05_sy_621.bin MN:AP9631 HR:05 SN: 5A1211T04371 MD:03/15/2012) (Embedded PowerNet SNMP Agent SW v2.2 compatible)
i want to battery monitor but do not bring me the query
i download of the pag www.apc.com the mib file to this ups "PowerNet MIB v4.1.4" but the oid 1.3.6.1.2.1.33.1.2 not responding and any of upsbattery, upsInput , upsOuput
i run a command snmpwalk but it does not return any data of the battery, the oids of mib are different from shown by the snmpwalk command
oid mibs
![]() ![]() ![]() |
1.3.6.1.2.1.33.1.1 | OBJECT IDENTIFIER |
![]() ![]() ![]() ![]() |
1.3.6.1.2.1.33.1.1.1 | OBJECT-TYPE |
![]() ![]() ![]() ![]() |
1.3.6.1.2.1.33.1.1.2 | OBJECT-TYPE |
![]() ![]() ![]() ![]() |
1.3.6.1.2.1.33.1.1.3 | OBJECT-TYPE |
![]() ![]() ![]() ![]() |
1.3.6.1.2.1.33.1.1.4 | OBJECT-TYPE |
![]() ![]() ![]() ![]() |
1.3.6.1.2.1.33.1.1.5 | OBJECT-TYPE |
![]() ![]() ![]() ![]() |
1.3.6.1.2.1.33.1.1.6 | OBJECT-TYPE |
![]() ![]() ![]() |
1.3.6.1.2.1.33.1.2 | OBJECT IDENTIFIER |
![]() ![]() ![]() ![]() |
1.3.6.1.2.1.33.1.2.1 | OBJECT-TYPE |
![]() ![]() ![]() ![]() |
1.3.6.1.2.1.33.1.2.2 | OBJECT-TYPE |
![]() ![]() ![]() ![]() |
1.3.6.1.2.1.33.1.2.3 | OBJECT-TYPE |
![]() ![]() ![]() ![]() |
1.3.6.1.2.1.33.1.2.4 | OBJECT-TYPE |
![]() ![]() ![]() ![]() |
1.3.6.1.2.1.33.1.2.5 | OBJECT-TYPE |
![]() ![]() ![]() ![]() |
1.3.6.1.2.1.33.1.2.6 | OBJECT-TYPE |
![]() ![]() ![]() ![]() |
1.3.6.1.2.1.33.1.2.7 | OBJECT-TYPE |
![]() ![]() ![]() |
1.3.6.1.2.1.33.1.3 | OBJECT IDENTIFIER |
![]() ![]() ![]() ![]() |
1.3.6.1.2.1.33.1.3.1 | OBJECT-TYPE |
![]() ![]() ![]() ![]() |
1.3.6.1.2.1.33.1.3.2 |
oid snmpwalk
.1.3.6.1.2.1.4.31.3.1.43.1.1 = 0
.1.3.6.1.2.1.4.31.3.1.43.1.2 = 0
.1.3.6.1.2.1.4.31.3.1.43.2.1 = 0
.1.3.6.1.2.1.4.31.3.1.43.2.2 = 0
.1.3.6.1.2.1.4.33.1.3.1.4.10.1.50.9 = 2
.1.3.6.1.2.1.4.33.1.3.1.4.127.0.0.1 = 1
.1.3.6.1.2.1.4.33.1.4.1.4.10.1.50.9 = 1
.1.3.6.1.2.1.4.33.1.4.1.4.127.0.0.1 = 1
.1.3.6.1.2.1.4.33.1.6.1.4.10.1.50.9 = 2
.1.3.6.1.2.1.4.33.1.6.1.4.127.0.0.1 = 2
.1.3.6.1.2.1.4.33.1.7.1.4.10.1.50.9 = 1
.1.3.6.1.2.1.4.33.1.7.1.4.127.0.0.1 = 1
.1.3.6.1.2.1.4.33.1.8.1.4.10.1.50.9 = 0
.1.3.6.1.2.1.4.33.1.8.1.4.127.0.0.1 = 0
.1.3.6.1.2.1.4.33.1.9.1.4.10.1.50.9 = 0
.1.3.6.1.2.1.4.33.1.9.1.4.127.0.0.1 = 0
.1.3.6.1.2.1.4.34.1.4.2.1.4.10.1.50.1 = 1125014280
.1.3.6.1.2.1.4.34.1.4.2.1.4.10.1.50.34 = -1168748544
.1.3.6.1.2.1.4.34.1.5.2.1.4.10.1.50.1 = .0
.1.3.6.1.2.1.4.34.1.5.2.1.4.10.1.50.34 = .0
.1.3.6.1.2.1.4.34.1.6.2.1.4.10.1.50.1 = 3
i dont know why
Posted: 2021-07-08 12:16 AM
This was originally posted on APC forums on 4/6/2015
hello angela. i am using debian 7.8 to the snmpwalk it has worked well with the other mib. installed the same way. but for some reason does not work with oid 1.3.6.1.4.1.318 when i run it returns me that
SNMPv2-SMI::enterprises.318.1.1.1.8.1.0 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.3.1.2.1.1.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.3.1.2.2.1.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.1.2 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.2.1 = STRING: "Temp Sensor 1"
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.2.2 = STRING: "Temp Sensor 2"
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.3.1 = INTEGER: 40
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.3.2 = INTEGER: 40
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.4.1 = INTEGER: 10
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.4.2 = INTEGER: 10
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.5.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.5.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.6.1 = INTEGER: 60
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.6.2 = INTEGER: 60
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.7.1 = INTEGER: 30
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.7.2 = INTEGER: 30
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.8.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.8.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.9.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.9.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.10.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.10.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.11.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.11.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.12.1 = INTEGER: 60
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.12.2 = INTEGER: 60
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.13.1 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.13.2 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.14.1 = INTEGER: 90
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.14.2 = INTEGER: 90
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.15.1 = INTEGER: 10
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.15.2 = INTEGER: 10
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.16.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.16.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.17.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.17.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.18.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.18.2 = INTEGER: 1
it is as if no work with powernet-mib. sorry for my English
Posted: 2021-07-08 12:15 AM
This reply was originally posted by Angela on APC forums on 4/6/2015
The OIDs you're referencing are for the RFC1628 MIB which is a generic Uninterruptible Power Supply MIB.
Please refer to additional information here if your intent is to use this generic non-APC MIB -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156148
If you want to use the APC PowerNet MIB, then you need to load it into your SNMP tool and you need to watch out of the syntax but all of the APC data is in the '318' enterprise and would be everything beyond .1.3.6.1.4.1.318.
If you need further help, please provide the specifics of what SNMP tool/MIB browser you're using and any commands. To me, it sounds like the APC PowerNet MIB is not properly loaded/compiled in your tool.
Posted: 2021-07-08 12:16 AM
This was originally posted on APC forums on 4/6/2015
hello angela. i am using debian 7.8 to the snmpwalk it has worked well with the other mib. installed the same way. but for some reason does not work with oid 1.3.6.1.4.1.318 when i run it returns me that
SNMPv2-SMI::enterprises.318.1.1.1.8.1.0 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.3.1.2.1.1.0 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.3.1.2.2.1.0 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.1.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.1.2 = INTEGER: 2
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.2.1 = STRING: "Temp Sensor 1"
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.2.2 = STRING: "Temp Sensor 2"
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.3.1 = INTEGER: 40
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.3.2 = INTEGER: 40
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.4.1 = INTEGER: 10
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.4.2 = INTEGER: 10
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.5.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.5.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.6.1 = INTEGER: 60
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.6.2 = INTEGER: 60
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.7.1 = INTEGER: 30
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.7.2 = INTEGER: 30
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.8.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.8.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.9.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.9.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.10.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.10.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.11.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.11.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.12.1 = INTEGER: 60
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.12.2 = INTEGER: 60
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.13.1 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.13.2 = INTEGER: 0
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.14.1 = INTEGER: 90
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.14.2 = INTEGER: 90
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.15.1 = INTEGER: 10
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.15.2 = INTEGER: 10
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.16.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.16.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.17.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.17.2 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.18.1 = INTEGER: 1
SNMPv2-SMI::enterprises.318.1.1.10.1.2.2.1.18.2 = INTEGER: 1
it is as if no work with powernet-mib. sorry for my English