adress the NMC

Solved
constant_W._apc
Ensign
Ensign
0 Likes
1
65

adress the NMC

This was originally posted on APC forums on 6/20/2012


hello,
i want to manage my SUA5000RMIU. i downloaded the PCNS (powerChute network shutdown) and the PCBE (powerChute business edition), but no one does connect to my UPS.

when i installed PCNS, it asked me the adress of the NMC. how could i adress my NMC. it 's needed to establish connection with the UPS.

thanking you in anticipation.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
65

Re: adress the NMC

This reply was originally posted by Bernard on APC forums on 6/20/2012


Good day! If you want to use PCBE to manage and monitor your UPS, you'll need to connect either the USB A to B cable or the serial cable (940-0024) that came with the unit from the UPS to your server. This is used so that the UPS can communicate with your computer. More information about how to install and what operating systems are compatible with PCBE can be found here PCNS needs a network management card to work and is only responsible for gracefully shutting down your servers. PCBE does both UPS management and graceful shutdown of the connected PC.

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
66

Re: adress the NMC

This reply was originally posted by Bernard on APC forums on 6/20/2012


Good day! If you want to use PCBE to manage and monitor your UPS, you'll need to connect either the USB A to B cable or the serial cable (940-0024) that came with the unit from the UPS to your server. This is used so that the UPS can communicate with your computer. More information about how to install and what operating systems are compatible with PCBE can be found here PCNS needs a network management card to work and is only responsible for gracefully shutting down your servers. PCBE does both UPS management and graceful shutdown of the connected PC.