Using USB to RS232 to connect SC 450VA to a QNAP

Solved
work2survive_apc
Cadet
0 Likes
1
193

Using USB to RS232 to connect SC 450VA to a QNAP

This was originally posted on APC forums on 12/4/2019


Using USB to RS232 adapter to connect SC 450VA to a QNAP?

Not sure in which section post this, my issue is the next:

My company owns a UPS 450VA which comes with a RS232 port as only communication port, and a QNAP TS-453BU-RP-4G

Does make sense to use an USB to RS232 adaptor in order to get the auto-protection running in the QNAP?
There is any other solution? Any technical spec for the Adapter?

Thanks.
APC Smart-UPS SC 450VA 230V
https://www.apc.com/shop/id/en/products/APC-Smart-UPS-SC-450VA-230V-1U-Rackmount-Tower/P-SC450RMI1U 

USB to RS232 adapter on Amazon.de
https://www.amazon.de/dp/B00QUZY4UG/ref=sr_1_3?keywords=USB+RS232&qid=1575449525&sr=8-3

UPS dialog on the QNAP
Attachments

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
193

Re: Using USB to RS232 to connect SC 450VA to a QNAP

This reply was originally posted by Bill on APC forums on 12/4/2019


Hello,

I recommend you get a UPS that offers USB support. Even with a USB to serial converter the UPS will not communicate with the USB on the QNAP. The converter cable is designed to create a serial port not convert serial to USB. 

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
194

Re: Using USB to RS232 to connect SC 450VA to a QNAP

This reply was originally posted by Bill on APC forums on 12/4/2019


Hello,

I recommend you get a UPS that offers USB support. Even with a USB to serial converter the UPS will not communicate with the USB on the QNAP. The converter cable is designed to create a serial port not convert serial to USB.