Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
80979members
347159posts

Use "PowerChute Network Shutdown" with "APEC SUA1500RMI 2U" UPS ?

Solved
jerome_apc
Cadet
0 Likes
1
94

Use "PowerChute Network Shutdown" with "APEC SUA1500RMI 2U" UPS ?

This was originally posted on APC forums on 4/25/2014


Hi,

I have to a clustor of servers with VMware vSphere Entreprise. The HA (High Availability) mode is activated.

I have two UPS "APEC SUA1500RMI 2U" and I'd like that in case of power failure the UPS are able request to vCenter to properly shutdown all the VM.

According to the APC site, I think that I need to buy:

- one "UPS Network Management Card 2 (AP9630)" by UPS

- one "PowerChute Network Shutdown" licence

("PowerChute Business Edition" seems to be uncompatible with VMware HA mode)

But, I'd like to know if the "APEC SUA1500RMI 2U" are compatible with "PowerChute Network Shutdown". Can someone help me?

Thanks,

Jerome


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
94

Re: Use "PowerChute Network Shutdown" with "APEC SUA1500RMI 2U" UPS ?

This reply was originally posted by Angela on APC forums on 4/25/2014


Hello,

I can at least say that your UPS model will work with AP9630 or AP9631 Network Management Card 2 and those cards work with PowerChute Network Shutdown. You may just want to verify that your version is compatible with PowerChute Network Shutdown v3.1 which is the current version. Here is the compatibility chart -> http://www.apcmedia.com/salestools/SJHN-7AYQNP/SJHN-7AYQNP_R49_EN.pdf

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
95

Re: Use "PowerChute Network Shutdown" with "APEC SUA1500RMI 2U" UPS ?

This reply was originally posted by Angela on APC forums on 4/25/2014


Hello,

I can at least say that your UPS model will work with AP9630 or AP9631 Network Management Card 2 and those cards work with PowerChute Network Shutdown. You may just want to verify that your version is compatible with PowerChute Network Shutdown v3.1 which is the current version. Here is the compatibility chart -> http://www.apcmedia.com/salestools/SJHN-7AYQNP/SJHN-7AYQNP_R49_EN.pdf