APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:48 AM . Last Modified: 2 weeks ago
My UPS800 has started continuously cycling between "On Line" and "Battery" even if nothing is connected. What does this mean? The batteries were replaced within the past six months.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:48 AM . Last Modified: 2 weeks ago
Do you have a USB cable plugged into the USB data port on the UPS (which the other end is the USB that connects to your computer)? If so, we could use PowerChute Personal Edition to see what is happening during this time on the UPS side.
Basically what I would do is clarify if anything has happened recently as I noted (power outage/surge, etc), and then turn the UPS off and unplug it from AC power. (Remove any other communication cables, if present.) Then, disconnect the battery temporarily and hold down the power button for 10-15 seconds. Reconnect the battery. Plug the UPS back in and turn it on and observe if any change in behavior.
If that doesn't help and especially if you cannot use PowerChute for some reason, you could go ahead and lower the UPS sensitivity as one step. If you do have PowerChute, the sensitivity option will be present there. If not, the steps to adjust the sensitivity without software are available in the user's guide, here -> http://www.apcmedia.com/salestools/ASTE-6Z7V3J/ASTE-6Z7V3J_R0_EN.pdf (refer to PDF page 2, and the section entitled: TRANSFER VOLTAGE AND SENSITIVITY ADJUSTMENT. You basically plug in the UPS but leave it turned off and hold down the power button and use the LEDs to change the setting.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:48 AM . Last Modified: 2 weeks ago
Can you clarify which specific model? This is located on the back or bottom of the UPS on a white sticker.
Usually this would be related to an input power problem potentially - did anything change recently where this UPS is plugged in or was there a recent power outage for example?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:48 AM . Last Modified: 2 weeks ago
It is model BL800BLK.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:48 AM . Last Modified: 2 weeks ago
I'm sorry. It is model BR800BLK.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:48 AM . Last Modified: 2 weeks ago
Do you have a USB cable plugged into the USB data port on the UPS (which the other end is the USB that connects to your computer)? If so, we could use PowerChute Personal Edition to see what is happening during this time on the UPS side.
Basically what I would do is clarify if anything has happened recently as I noted (power outage/surge, etc), and then turn the UPS off and unplug it from AC power. (Remove any other communication cables, if present.) Then, disconnect the battery temporarily and hold down the power button for 10-15 seconds. Reconnect the battery. Plug the UPS back in and turn it on and observe if any change in behavior.
If that doesn't help and especially if you cannot use PowerChute for some reason, you could go ahead and lower the UPS sensitivity as one step. If you do have PowerChute, the sensitivity option will be present there. If not, the steps to adjust the sensitivity without software are available in the user's guide, here -> http://www.apcmedia.com/salestools/ASTE-6Z7V3J/ASTE-6Z7V3J_R0_EN.pdf (refer to PDF page 2, and the section entitled: TRANSFER VOLTAGE AND SENSITIVITY ADJUSTMENT. You basically plug in the UPS but leave it turned off and hold down the power button and use the LEDs to change the setting.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:48 AM . Last Modified: 2 weeks ago
I have looked and looked, but I cannot find a USB port on my APC UPS. Am I completely crazy? I did disconnect the battery and press the power switch for 15 or 20 seconds. After reconnecting, it still cycles between "on line" and "on battery." I am plugged into a different outlet out in the garage with the same symptoms.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:48 AM . Last Modified: 2 weeks ago
I found the right cable and am now connected. However, in order to run PowerChute, it says I need to quit System Preferences and restart it. I cannot seem to do that. The APC information is showing that the unit is actually going on battery, however.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:48 AM . Last Modified: 2 weeks ago
I was able to lower the sensitivity using the process you referred me to (manually). It appears to be working okay now. Thank you very much!
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.