Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79125members
343511posts

UPS upgrade

Solved
kzsolt_apc
Crewman
Crewman
0 Likes
6
175

UPS upgrade

This was originally posted on APC forums on 4/10/2016


Dear Everybody!

We try to upgrade UPS form SC620 to SMX750. In theory both have serial smart interface, so we need just replace UPS form old to new one.

But in practice SC has DB9 connector, SMX has RJ45 connector. Looks like this major difference, because PowerChuteBE handle it in a different way.

It is no way to configure UPS smart connector type, and no way to refresh/reinstall PowerChuteBE.

Therefore no way to upgrade from SC to (e.g.) SMX UPS!?

Our UPSs driven SLES servers.

Any idea?


Accepted Solutions
kzsolt_apc
Crewman
Crewman
0 Likes
0
175

Re: UPS upgrade

This was originally posted on APC forums on 4/14/2016


Reinstall looks like work in test environment, I try to do it in a hot systems.

See Answer In Context

6 Replies 6
BillP
Administrator Administrator
Administrator
0 Likes
0
176

Re: UPS upgrade

This reply was originally posted by Bill on APC forums on 4/11/2016


Hi,

What version of SuSE Linux are the servers?

kzsolt_apc
Crewman
Crewman
0 Likes
0
176

Re: UPS upgrade

This was originally posted on APC forums on 4/11/2016


Sorry, SLES 11.

BillP
Administrator Administrator
Administrator
0 Likes
0
176

Re: UPS upgrade

This reply was originally posted by Bill on APC forums on 4/12/2016


Hi,

You should uninstall the version of PowerChute that is running, attach the serial cable that shipped with the SMT750 (SKU 940-0625), download the latest version of PowerChute from APC.com, and install the new version. 

kzsolt_apc
Crewman
Crewman
0 Likes
0
176

Re: UPS upgrade

This was originally posted on APC forums on 4/13/2016


On 4/12/2016 3:13 PM, Bill said:

uninstall the version of PowerChute that is running

But there is no description (way) how to do this for linux/unix type operating system.

I found some description from windows, but is is useless for other kind of operating system.

BillP
Administrator Administrator
Administrator
0 Likes
0
176

Re: UPS upgrade

This reply was originally posted by Bill on APC forums on 4/13/2016


Hi,

To remove PowerChute Business Edition open a terminal window and type sudo rpm -e pbeagent

kzsolt_apc
Crewman
Crewman
0 Likes
0
176

Re: UPS upgrade

This was originally posted on APC forums on 4/14/2016


Reinstall looks like work in test environment, I try to do it in a hot systems.