Hi all,
I have to change UPS which works in VM environment. Is it possible just to move NMC APC 9630 from old to the new one ? Will IP and PowerChute "Authentication Phrase" be kept ? I want to avoid completely new configuration.
Thx in advance for help.
Lech
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:50 AM . Last Modified: 2024-02-29 10:30 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:50 AM . Last Modified: 2024-02-29 10:30 PM
Hi,
On 10/23/2015 4:39 AM, Lech said:I have to change UPS which works in VM environment. Is it possible just to move NMC APC 9630 from old to the new one ? Will IP and PowerChute "Authentication Phrase" be kept ? I want to avoid completely new configuration.
Yes. You can move the NMC to the new UPS and the user name, password, and authentication phrase will remain. You will need to make changes to the any outlet group settings and should review the shutdown settings.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:50 AM . Last Modified: 2024-02-29 10:30 PM
Thanks Bill, so I will try this way.
Lech