Hello,
we have Symmetra LX 16000 UPS. There are 2 power modules 8KVA, 2 intelligence modules and 2 battery modules.
The load is just about 10%.
As we wanted to check how long will it run on battery, we switched off the main power to the UPS.
After a few seconds, the output was switched off unexpectedly. We switched on the main power than.
There is a part of log and data below (unfortunately, the data are logged every 10mins only, there is nothing to check for the time of error).
Can anybody please explain what happened? Why was the output power turned off?
....
....
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:33 AM . Last Modified: 2 weeks ago
Thanks for your reply. UPS is out of warranty.
We opened the battery pack and checked each battery. In both packs, there was one battery that showed 13V without the load, but under the load it showed 0. All others were OK. After replacing those defective batteries everything runs ok.
How is it possible, that UPS did not recognize that during self tests?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:33 AM . Last Modified: 2 weeks ago
1. Check that the batteries are ok and well connected.
2. If 1 above if confirmed ok, then there's an internal fault
3. If under warranty take it to where you bought it but if not under warranty, snap the panel clearly showing the component label and send to me
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:33 AM . Last Modified: 2 weeks ago
Thanks for your reply. UPS is out of warranty.
We opened the battery pack and checked each battery. In both packs, there was one battery that showed 13V without the load, but under the load it showed 0. All others were OK. After replacing those defective batteries everything runs ok.
How is it possible, that UPS did not recognize that during self tests?
Link copied. Please paste this link to share this article on your social media post.