Posted: 2021-08-15 09:02 AM
Hello,
I have the problem that the network card does not recognize the UPS.
Can someone help me or tell me what is wrong here.
I attach a few screenshots with.
PS: Smart UPS 750
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-16 05:42 AM
The wrong firmware is on the card and therefore it will not recognize the UPS.
For a Smart-UPS 750 you should install the latest version from this link
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-17 01:08 AM
Great. Thanks a lot!!
It works.
However, I still have a small problem.
I have selected in the firmware update software that the German language is also installed.
Now there is only English on it.
How can I still get the German language on it?
Thanks a lot
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-24 11:33 AM
There's a language pack that you need to install if you want languages other than English.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.