UPS 120Vac

This was originally posted on APC forums on 5/27/2009


Hi,

Does [SUVTP10KF3B4|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUVTP10KF3B4&tab=models&total_watts=...] have as an output voltage 120Vac? I know its output is 3 phase 208Vac, but I want to be sure if the voltage PH-N is 120Vac because the installation and operation manual don't say it.

And what should I need if I want to install a Symmetra LX @ 120Vac ( [SYA12K16P|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SYA12K16P&total_watts=500] ) and if I have as an input 3 phase 220Vac (3 PH and GND, no N, voltage PH-PH 220Vac), maybe an isolation transformer with what specifications?

HA


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
88

Re: UPS 120Vac

This reply was originally posted by Angela on APC forums on 5/27/2009


the [tech specs|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUVTP10KF3B4] on the product page for that UPS say:

Nominal Output Voltage: 120V,208V,208V 3PH

In regards to the Symmetra LX for the US, so the model you posted, SYA12K16P, accepts an input of two phases (208v or 240v), a neutral, and a ground. It is looking for 208v or 240v nominal voltages. [this probably answers some questions too|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=7059]

also, take a look at [this article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=6929] pertaining to the importance of a neutral.

on the INTERNATIONAL UNIT, so SYA12K16I, the wiring is below:

Nominal Input Voltage 230V,400V 3PH
Input Frequency 45 - 65 Hz (auto sensing)
Input Connections
Hard Wire 3 wire (1PH+N+G)
Hard Wire 5-wire (3PH + N + G)

hope that helps!

See Answer In Context

2 Replies 2
HemeAqui_apc
Ensign
Ensign
0 Likes
0
88

Re: UPS 120Vac

This was originally posted on APC forums on 5/27/2009


Yes it helps. Then the SUVT has an output voltage of 120Vac. Thanks, I wasn't sure because the manual doesn't say anything about that and I'm not familiar with UPS @ 120Vac.

And about the Symmetra LX, I don't understand that electrical configuration: 2PH, N, G. I know in 3 phase 2 posibles configurations:

1- 3PH and G, for example in 220Vac, voltage ph-ph 220Vac and with a floating ground
2- 3PH, N and G, for example in 220Vac, voltage ph-ph 380Vac, voltage ph-n 220Vac and voltage n-g 0Vac

So I have a 3PH and GND of 220Vac and what I need if I want to feed the Symmetra with this configuration, what kind of isolation transformer, or is it imposible to do that? Let me know if it isn't clear.

HA

BillP
Administrator Administrator
Administrator
0 Likes
0
89

Re: UPS 120Vac

This reply was originally posted by Angela on APC forums on 5/27/2009


the [tech specs|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SUVTP10KF3B4] on the product page for that UPS say:

Nominal Output Voltage: 120V,208V,208V 3PH

In regards to the Symmetra LX for the US, so the model you posted, SYA12K16P, accepts an input of two phases (208v or 240v), a neutral, and a ground. It is looking for 208v or 240v nominal voltages. [this probably answers some questions too|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=7059]

also, take a look at [this article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=6929] pertaining to the importance of a neutral.

on the INTERNATIONAL UNIT, so SYA12K16I, the wiring is below:

Nominal Input Voltage 230V,400V 3PH
Input Frequency 45 - 65 Hz (auto sensing)
Input Connections
Hard Wire 3 wire (1PH+N+G)
Hard Wire 5-wire (3PH + N + G)

hope that helps!