Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79290members
343968posts

The Application Was Not Able to Load

Solved
BillP
Administrator Administrator
Administrator
0 Likes
4
334

The Application Was Not Able to Load

This question was originally posted by Walter on APC forums on 9/10/2020


Hi,

after updating a Management Card 2 from 6.8x to 6.88 with file: apc_hw05_aos688_sumx688_bootmon109.exe, I cant login via web interface, I always see this error message: 

The Application Was Not Able to Load.

You are attempting to access a Schneider device.
There was a problem loading the application. Please login to the device via telnet for more details. 

Telnet login works:

Schneider Electric Network Management Card AOS v6.8.8
(c) Copyright 2020 All Rights Reserved
-------------------------------------------------------------------------------
Name : xxxxxxxxxx Date : 09/10/2020
Contact : Walter xxxxxxxx Time : 13:12:02
Location : Unknown User : Super User
Up Time : 0 Days 0 Hours 32 Minutes Stat : P+ N4+ N6+ A-
-------------------------------------------------------------------------------
IPv4 : Enabled IPv6 : Enabled
Ping Response : Enabled
-------------------------------------------------------------------------------
HTTP : Enabled HTTPS : Enabled
FTP : Enabled Telnet : Enabled
SSH/SCP : Enabled SNMPv1 : Read/Write
SNMPv3 : Disabled
-------------------------------------------------------------------------------
Super User : Enabled RADIUS : Disabled
Administrator : Disabled Device User : 1 Enabled
Read-Only User : 1 Enabled Network-Only User : Disabled

 

apc>about
E000: Success
Hardware Factory
---------------
Model Number: AP9631CH
Serial Number: 5A1708Txxxxx
Hardware Revision: 05
Manufacture Date: 02/20/2017
MAC Address: 00 C0 B7 xxxxxxx
Management Uptime: 0 Days 0 Hours 33 Minutes

Application Module
---------------
Name: aos
Version: v6.8.8
Date: Apr 28 2020
Time: 17:21:52

APC OS(AOS)
---------------
Name: aos
Version: v6.8.8
Date: Apr 28 2020
Time: 17:21:52

APC Boot Monitor
---------------
Name: bootmon
Version: v1.0.9
Date: Mar 27 2019
Time: 16:23:06

 

Manual states A- is an check sum error in Application, so I tried to flash the application:

Unfortunately the ftp transfer never starts:

C:\temp\xxx\apc_hw05_aos688_sumx688_bootmon109\Bins>ftp xxxxxxxxxxxx
Verbindung mit xxxxxxxxxxxx wurde hergestellt.
220 AP9631CH Network Management Card AOS v6.8.8 FTP server ready.
550 NOOP requested action not taken.
Benutzer (xxxxxxxxxxxxxxxxx:(none)): apc
331 User name okay, need password.
Kennwort:
230 User logged in, proceed.
ftp> bin
200 TYPE Command okay.
ftp> hash
Hashmarkierungsdruck EIN FTP: (2048 Bytes/Hash).
ftp> put apc_hw05_sumx_688.bin
200 PORT Command okay.
150 File status okay; about to open data connection.

Here the ftp connection hangs forever. 

Any ideas how to recover this management card? 

Walter

 

 

  

 

 


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
334

Re: The Application Was Not Able to Load

This reply was originally posted by Gavan on APC forums on 9/16/2020


Hi Walter,

Can you try using the WinSCP client? Sometimes there can be compatibility issues with different clients.

https://winscp.net/eng/index.php 

-Gavan

See Answer In Context

4 Replies 4
BillP
Administrator Administrator
Administrator
0 Likes
0
334

Re: The Application Was Not Able to Load

This reply was originally posted by Bill on APC forums on 9/10/2020


Hi,

If you cannot recover via FTP you may need to recover via the boot monitor. See Schneider Electric FAQ FA293874

BillP
Administrator Administrator
Administrator
0 Likes
0
334

Re: The Application Was Not Able to Load

This reply was originally posted by Walter on APC forums on 9/11/2020


Bill,

next week I am with customer again, so I will try next week and come back. 

Happy weekend. 

Walter

BillP
Administrator Administrator
Administrator
0 Likes
0
335

Re: The Application Was Not Able to Load

This reply was originally posted by Gavan on APC forums on 9/16/2020


Hi Walter,

Can you try using the WinSCP client? Sometimes there can be compatibility issues with different clients.

https://winscp.net/eng/index.php 

-Gavan

BillP
Administrator Administrator
Administrator
0 Likes
0
334

Re: The Application Was Not Able to Load

This reply was originally posted by Walter on APC forums on 9/19/2020


Gavan,

thank you, I transferred the application (sumx) with scp and now the NMC2 works again. 

Walter