Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
You can subscribe to this forum after you log in or create your free account..
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
Posted: 2021-06-30 06:00 AM
This question was originally posted by Walter on APC forums on 9/10/2020
Hi,
after updating a Management Card 2 from 6.8x to 6.88 with file: apc_hw05_aos688_sumx688_bootmon109.exe, I cant login via web interface, I always see this error message:
The Application Was Not Able to Load.
You are attempting to access a Schneider device.
There was a problem loading the application. Please login to the device via telnet for more details.
Telnet login works:
Schneider Electric Network Management Card AOS v6.8.8
(c) Copyright 2020 All Rights Reserved
-------------------------------------------------------------------------------
Name : xxxxxxxxxx Date : 09/10/2020
Contact : Walter xxxxxxxx Time : 13:12:02
Location : Unknown User : Super User
Up Time : 0 Days 0 Hours 32 Minutes Stat : P+ N4+ N6+ A-
-------------------------------------------------------------------------------
IPv4 : Enabled IPv6 : Enabled
Ping Response : Enabled
-------------------------------------------------------------------------------
HTTP : Enabled HTTPS : Enabled
FTP : Enabled Telnet : Enabled
SSH/SCP : Enabled SNMPv1 : Read/Write
SNMPv3 : Disabled
-------------------------------------------------------------------------------
Super User : Enabled RADIUS : Disabled
Administrator : Disabled Device User : 1 Enabled
Read-Only User : 1 Enabled Network-Only User : Disabled
apc>about
E000: Success
Hardware Factory
---------------
Model Number: AP9631CH
Serial Number: 5A1708Txxxxx
Hardware Revision: 05
Manufacture Date: 02/20/2017
MAC Address: 00 C0 B7 xxxxxxx
Management Uptime: 0 Days 0 Hours 33 Minutes
Application Module
---------------
Name: aos
Version: v6.8.8
Date: Apr 28 2020
Time: 17:21:52
APC OS(AOS)
---------------
Name: aos
Version: v6.8.8
Date: Apr 28 2020
Time: 17:21:52
APC Boot Monitor
---------------
Name: bootmon
Version: v1.0.9
Date: Mar 27 2019
Time: 16:23:06
Manual states A- is an check sum error in Application, so I tried to flash the application:
Unfortunately the ftp transfer never starts:
C:\temp\xxx\apc_hw05_aos688_sumx688_bootmon109\Bins>ftp xxxxxxxxxxxx
Verbindung mit xxxxxxxxxxxx wurde hergestellt.
220 AP9631CH Network Management Card AOS v6.8.8 FTP server ready.
550 NOOP requested action not taken.
Benutzer (xxxxxxxxxxxxxxxxx:(none)): apc
331 User name okay, need password.
Kennwort:
230 User logged in, proceed.
ftp> bin
200 TYPE Command okay.
ftp> hash
Hashmarkierungsdruck EIN FTP: (2048 Bytes/Hash).
ftp> put apc_hw05_sumx_688.bin
200 PORT Command okay.
150 File status okay; about to open data connection.
Here the ftp connection hangs forever.
Any ideas how to recover this management card?
Walter
Posted: 2021-06-30 06:00 AM
This reply was originally posted by Gavan on APC forums on 9/16/2020
Hi Walter,
Can you try using the WinSCP client? Sometimes there can be compatibility issues with different clients.
https://winscp.net/eng/index.php
-Gavan
Posted: 2021-06-30 06:00 AM
This reply was originally posted by Bill on APC forums on 9/10/2020
Hi,
If you cannot recover via FTP you may need to recover via the boot monitor. See Schneider Electric FAQ FA293874
Posted: 2021-06-30 06:00 AM
This reply was originally posted by Walter on APC forums on 9/11/2020
Bill,
next week I am with customer again, so I will try next week and come back.
Happy weekend.
Walter
Posted: 2021-06-30 06:00 AM
This reply was originally posted by Gavan on APC forums on 9/16/2020
Hi Walter,
Can you try using the WinSCP client? Sometimes there can be compatibility issues with different clients.
https://winscp.net/eng/index.php
-Gavan
Posted: 2021-06-30 06:00 AM
This reply was originally posted by Walter on APC forums on 9/19/2020
Gavan,
thank you, I transferred the application (sumx) with scp and now the NMC2 works again.
Walter
User | Count |
---|---|
4834 | |
190 | |
111 | |
108 | |
67 | |
63 |
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.