APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:26 AM . Last Modified: 2024-03-19 02:22 AM
Hi, I want to know if a SY200K250D can be expanded to a 250kVA/KW configuration and what modules would I have to add?
Or do I have to change frames and go with the SY250K500D?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:26 AM . Last Modified: 2024-03-19 02:22 AM
You should have at least 1.6 batterymodules (1 module = 1 row = 6 units) per powermodule.
So, 10 powermodules require minimum 10 x 1.6 = 16 modules = 2 full battery frames.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:26 AM . Last Modified: 2024-03-19 02:22 AM
So long as your site wiring was for the 250kw load, it should have two empty slots for 25KW modules.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:26 AM . Last Modified: 2024-03-19 02:22 AM
Yes i can be expanded upto 250kVA/KW . But if your load will be between ( 225-250KVA/KW) then it will not be internal redundant.
You simply need to add SYPM25KD Qty 02/-
Here is link for more information
http://www.apc.com/shop/pk/en/products/APC-Symmetra-PX-25kW-Power-Module-400-480V/P-SYPM25KD
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:26 AM . Last Modified: 2024-03-19 02:22 AM
Thanks for your reply.
Do I need to add any battery modules?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:26 AM . Last Modified: 2024-03-19 02:22 AM
You should have at least 1.6 batterymodules (1 module = 1 row = 6 units) per powermodule.
So, 10 powermodules require minimum 10 x 1.6 = 16 modules = 2 full battery frames.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.