I have a symmetra lx and working batteries, i have measured all the voltages, but when i put them in they read as faulty. through my research, it seems it may be because the battery module or casing is older than three years, and i want to know how to reset the date code so that the symmetra reads it as a new battery. The battery type i am using is SYBT5
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:24 PM . Last Modified: 2024-02-29 11:58 PM
By your wording (use of word casing) - it sounds like you may have replaced the internal batteries within the battery module itself. This is not supported and has been known to cause a battery module to register as faulty.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:24 PM . Last Modified: 2024-02-29 11:58 PM
Aram,
The Symmetra would not mark a battery faulty based on an age of 3 years with everything else working fine. Common causes for battery failure flagging include calibration factor, heat, capacity, number of discharges, and a few other measurements. With that being said, there is no way to reset the date on the batteries.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 11:24 PM . Last Modified: 2024-02-29 11:58 PM
By your wording (use of word casing) - it sounds like you may have replaced the internal batteries within the battery module itself. This is not supported and has been known to cause a battery module to register as faulty.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.