Symmetra LX Bypass Dry Contact Output

Solved
BillP
Administrator Administrator
Administrator
0 Likes
2
109

Symmetra LX Bypass Dry Contact Output

This question was originally posted by Federico on APC forums on 4/19/2010


I'm in hurry trying to determine if there is a way to know when the external bypass of a symmetra LX is used with a dry contact Output.

Online Manuals lack detailed information.

Is there a way to extract a dry contact from this bypass: SBP16KRMI4U

Link:
http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SBP16KRMI4U&tab=models

Why? The symmetra LX has a major problem when going in bypass mode (static or manual). All the current goes through L1 so I'm left with two options, turn off the extra load with a trip coil circuit to protect wires or cut the power to the UPS (not possible).


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
109

Symmetra LX Bypass Dry Contact Output

This reply was originally posted by Federico on APC forums on 4/19/2010


I'm in hurry trying to determine if there is a way to know when the external bypass of a symmetra LX is used with a dry contact Output.

Online Manuals lack detailed information.

Is there a way to extract a dry contact from this bypass: SBP16KRMI4U

Link:
http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SBP16KRMI4U&tab=models

Why? The symmetra LX has a major problem when going in bypass mode (static or manual). All the current goes through L1 so I'm left with two options, turn off the extra load with a trip coil circuit to protect wires or cut the power to the UPS (not possible).

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
109

Re: Symmetra LX Bypass Dry Contact Output

This reply was originally posted by Federico on APC forums on 4/22/2010


Thanks, I checked this by myself yesterday after dismantling the unit. 😃

BillP
Administrator Administrator
Administrator
0 Likes
0
110

Symmetra LX Bypass Dry Contact Output

This reply was originally posted by Federico on APC forums on 4/19/2010


I'm in hurry trying to determine if there is a way to know when the external bypass of a symmetra LX is used with a dry contact Output.

Online Manuals lack detailed information.

Is there a way to extract a dry contact from this bypass: SBP16KRMI4U

Link:
http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SBP16KRMI4U&tab=models

Why? The symmetra LX has a major problem when going in bypass mode (static or manual). All the current goes through L1 so I'm left with two options, turn off the extra load with a trip coil circuit to protect wires or cut the power to the UPS (not possible).