Switched PDU

Solved
BillP
Administrator Administrator
Administrator
0 Likes
1
138

Switched PDU

This question was originally posted by Luis Fernando on APC forums on 6/18/2015


Hi, I have an AP7900 Switched PDU, and I was wondering if it's possible to configure a sequential OFF triggered by an event of power loss in the UPS powering the PDU.

On the other hand, I want to know what triggers the ON and OFF Delay configured per outlet on the Configuration Tab?

Thanks.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
138

Re: Switched PDU

This reply was originally posted by Angela on APC forums on 6/18/2015


Hello Luis,

Yes, Power on/off delays under Configuration tab will apply when input power is applied to the PDU from a cold start  (like when the UPS powering the PDU turns off and back on again) and it also applies if you select the on-delayed or off-delayed commands within the PDU itself. You can bypass those if you select on-immediate or off-immediate.

I hope this clarifies. Let us know if you have further questions.

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
139

Re: Switched PDU

This reply was originally posted by Angela on APC forums on 6/18/2015


Hello Luis,

Yes, Power on/off delays under Configuration tab will apply when input power is applied to the PDU from a cold start  (like when the UPS powering the PDU turns off and back on again) and it also applies if you select the on-delayed or off-delayed commands within the PDU itself. You can bypass those if you select on-immediate or off-immediate.

I hope this clarifies. Let us know if you have further questions.