Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79201members
343760posts

Smat-UPS with Network-Management-Card shall shutdown a NAS

Solved
BillP
Administrator Administrator
Administrator
0 Likes
3
94

Smat-UPS with Network-Management-Card shall shutdown a NAS

This question was originally posted by Jürgen on APC forums on 3/29/2016


Hallo,

I have a Smart-UPS (SMT1500I) with a Network-Management-Card (AP9631). On 2 Windows-Server is the PowerChute Network Shutdown-Software installed. It works fine.

One auf the Windows-Servers has an iSCSI-Drive on a NAS (Qnap TS-1079 Pro).

How must I configured the Network Shutdown-Software and the NAS to shutdown the NAS when the Power is off and the Sever shutdown?

The Qnap-NAS support an UPS via USB. But I read in the instruction of the UPS/Management-Card, that the USB-Port shall not use together with the Management-Card.

Thanks for information.

Juergen

Tags (2)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
94

Re: Smat-UPS with Network-Management-Card shall shutdown a NAS

This reply was originally posted by Bill on APC forums on 3/29/2016


Hi,

You can connect the NAS to the UPS using USB when there is a NMC installed. The reason it is said not to use both NMC and USB together is because some people will attempt to use the NMC and PowerChute Business Edition or APCUPSD together. The issue that can arise is the UPS can be controlled by the NMC and PowerChute Business Edition or APCUPSD. So users could theoretically be making configuration changes to the UPS simultaneously on the NMC and PowerChute Business Edition or APCUPSD which can cause issues. 

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
95

Re: Smat-UPS with Network-Management-Card shall shutdown a NAS

This reply was originally posted by Bill on APC forums on 3/29/2016


Hi,

You can connect the NAS to the UPS using USB when there is a NMC installed. The reason it is said not to use both NMC and USB together is because some people will attempt to use the NMC and PowerChute Business Edition or APCUPSD together. The issue that can arise is the UPS can be controlled by the NMC and PowerChute Business Edition or APCUPSD. So users could theoretically be making configuration changes to the UPS simultaneously on the NMC and PowerChute Business Edition or APCUPSD which can cause issues. 

BillP
Administrator Administrator
Administrator
0 Likes
0
94

Re: Smat-UPS with Network-Management-Card shall shutdown a NAS

This reply was originally posted by Jürgen on APC forums on 3/29/2016


Hi Bill,

thanks for the answer.

I´ll test it.

Jürgen

BillP
Administrator Administrator
Administrator
0 Likes
0
94

Re: Smat-UPS with Network-Management-Card shall shutdown a NAS

This reply was originally posted by Ben on APC forums on 3/30/2016


I guess in this case that simultaneous use of the NMC and USB connections will solve the problem. But generally speaking it would be great if there was a PCNS software package that could run on NASes like the QNAP.