APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:48 PM . Last Modified: 2024-03-06 10:37 PM
I just replaced my battery in a Smartups SC620 and the battery run time is incorrect. I was wondering if you could provide the battery constant for this model.
Thanks,
Dan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:48 PM . Last Modified: 2024-03-06 10:37 PM
Hi Daniel,
Unfortunately, we do not have the battery constant available. What you can try to do is run a manual runtime calibration. The instructions are below.
This is a manual procedure and should not be confused with the runtime calibration performed through PowerChute software. The batteries inside of the Smart-UPS are controlled by a microprocessor within the UPS. Sometimes it is necessary to reset this microprocessor, especially after the installation of new batteries.
Note: Before beginning the calibration make sure the UPS has been online and charging for at leat 24 hours for just the UPS or 48 hours for a UPS with external batteries.
1. Stop the PowerChute software from running and disconnect the serial cable.
2.There must be at least a 30% load attached to the UPS during this procedure, and this load cannot fluctuate more than +/- 5%. This process will cause the UPS to shut off and cut power to its outlets, therefore, attach a non-critical load to the UPS and then force the UPS on battery by disconnecting it from utility power.
3. Allow the unit to run on battery until it turns off completely. Make sure a 30% load or greater is present!
4. Plug the UPS back into the wall outlet and allow it to recharge (it will recharge more quickly turned off and with no load present). Once the unit has recharged, the ""runtime remaining"" calculation should be more accurate. Remember that if the unit is an older model, then the runtime will not improve significantly.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:48 PM . Last Modified: 2024-03-06 10:37 PM
Hi Daniel,
Unfortunately, we do not have the battery constant available. What you can try to do is run a manual runtime calibration. The instructions are below.
This is a manual procedure and should not be confused with the runtime calibration performed through PowerChute software. The batteries inside of the Smart-UPS are controlled by a microprocessor within the UPS. Sometimes it is necessary to reset this microprocessor, especially after the installation of new batteries.
Note: Before beginning the calibration make sure the UPS has been online and charging for at leat 24 hours for just the UPS or 48 hours for a UPS with external batteries.
1. Stop the PowerChute software from running and disconnect the serial cable.
2.There must be at least a 30% load attached to the UPS during this procedure, and this load cannot fluctuate more than +/- 5%. This process will cause the UPS to shut off and cut power to its outlets, therefore, attach a non-critical load to the UPS and then force the UPS on battery by disconnecting it from utility power.
3. Allow the unit to run on battery until it turns off completely. Make sure a 30% load or greater is present!
4. Plug the UPS back into the wall outlet and allow it to recharge (it will recharge more quickly turned off and with no load present). Once the unit has recharged, the ""runtime remaining"" calculation should be more accurate. Remember that if the unit is an older model, then the runtime will not improve significantly.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.