Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
80566members
346448posts

Smart ups XL5000

Solved
ugiannini_apc
Crewman
Crewman
0 Likes
6
193

Smart ups XL5000

This was originally posted on APC forums on 2/15/2016


Hi my ups has developed a faulty battery and i'm getting the following alert: At least 1 battery has failed. The ups has 6 batteries in total. How do i go about eliminating the faulty battery?


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
193

Re: Smart ups XL5000

This reply was originally posted by Bill on APC forums on 2/16/2016


Hi,

You would replace a SURT192XLBP with a new SUTR192XLBP. 

See Answer In Context

6 Replies 6
mitsmith_apc
Lt. Commander
Lt. Commander
0 Likes
0
193

Re: Smart ups XL5000

This was originally posted on APC forums on 2/15/2016


Hi Umberto,

What is the exact model number of the unit?

If you have battery packs attached the first thing I would do is disconnect them and run a self test. If it fails then you know it is at least one in the main unit. You can then take batteries from the battery pack and swap them with the main unit and run another self test. In general though if the batteries are pushing 5 years old I would recommend replacing all of them as mismatch batteries are not good for the system and can lead to unexpected performance. 

ugiannini_apc
Crewman
Crewman
0 Likes
0
193

Re: Smart ups XL5000

This was originally posted on APC forums on 2/16/2016


Thanks very much for that, i have a really silly question. I've spent a lot of time on the APC website with no success, i'm trying to find out what batteries this unit uses. I can't find the info anywhere. Are they RBC44?

ugiannini_apc
Crewman
Crewman
0 Likes
0
193

Re: Smart ups XL5000

This was originally posted on APC forums on 2/16/2016


Sorry i forgot to mention the Model Number is SURTD 5000XLI

BillP
Administrator Administrator
Administrator
0 Likes
0
193

Re: Smart ups XL5000

This reply was originally posted by Bill on APC forums on 2/16/2016


Hi,

The internal original battery pack SKU is RBC44 and it has been replaced with APCRBC140. The external battery packs SKU is SURT192XLBP. 

ugiannini_apc
Crewman
Crewman
0 Likes
0
193

Re: Smart ups XL5000

This was originally posted on APC forums on 2/16/2016


1 more silly question please,

So if it turns out that i have a faulty batter module in the SURT192XLBP unit which battery do i replace it with? will it be a RBC140?

Many Thanks

Umberto

BillP
Administrator Administrator
Administrator
0 Likes
0
194

Re: Smart ups XL5000

This reply was originally posted by Bill on APC forums on 2/16/2016


Hi,

You would replace a SURT192XLBP with a new SUTR192XLBP.