Posted: 2021-06-30 09:35 PM
This was originally posted on APC forums on 7/24/2016
Our Smart-UPS VT 10 kVA: ran a scheduled weekly self test, the test failed with 'A weak battery exists', contacted our UPS maintenance company who sent tech to site, he tested and could not fine the weak battery, in fact he said it was all good (waiting on report from tech who did the testing). we're still getting the alert every 2 minutes though for weak battery and self test failed ??, below are the SNMP traps being generated. Anyone seen this before? Tech thinks it may well be system generated alert has been triggered after X amount of time, UPS has been in production for about 2 years 8 months.
snmpTrapEnterprise = PowerNet-MIB:apc
experimental.1057.1.0 = 10.9.128.251
sysUpTime = 354 days 21 hours 36 minutes 55.30 seconds
snmpTrapOID = PowerNet-MIB:apc.0.3
mtrapargsString = UPS: Self-Test Failed
snmpTrapEnterprise = PowerNet-MIB:apc
experimental.1057.1.0 = 10.9.128.251
sysUpTime = 354 days 21 hours 36 minutes 52.80 seconds
snmpTrapOID = PowerNet-MIB:apc.0.77
mtrapargsInteger = 36
mtrapargsString = UPS: A weak battery exists.
Posted: 2021-06-30 09:35 PM
This reply was originally posted by Bill on APC forums on 7/25/2016
Paul,
When the tech was on site did he run a self-test and if so did it fail? If he did not run a self-test I suggest doing so to see if the error clears. You can run the self-test via the NMC.
Posted: 2021-06-30 09:35 PM
This reply was originally posted by Bill on APC forums on 7/25/2016
Paul,
When the tech was on site did he run a self-test and if so did it fail? If he did not run a self-test I suggest doing so to see if the error clears. You can run the self-test via the NMC.