Smart UPS & Smart UPS online

This question was originally posted by Rico on APC forums on 1/9/2020


Dear Folks,

Can Smart UPS provide the power to the load when it is off or in fault?

Can Smart UPS online provide the power to the load when it is off or in fault ?

Thanks,


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
132

Re: Smart UPS & Smart UPS online

This reply was originally posted by Matt on APC forums on 1/9/2020


Hi Rico

 

If there is utility power to the UPS then it is functioning, the output can be switched off but the UPS will be on, so there isn't really a shutdown state when utility power is present.

 

Regards

 

Matt

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
132

Re: Smart UPS & Smart UPS online

This reply was originally posted by Matt on APC forums on 1/9/2020


Hi

The Smart UPS online have a bypass feature, so as long as utility power is ok then it can provide power if the UPS has issues.

The Smart UPS are a line interactive topology and do not have a bypass feature, so will not provide power if the UPS has an issue.

 

Regards

 

Matt

 

BillP
Administrator Administrator
Administrator
0 Likes
0
130

Re: Smart UPS & Smart UPS online

This reply was originally posted by Rico on APC forums on 1/9/2020


Dear Matt,

thank you for your reply.

When the Smart UPS online is in shutdown state, can the utility power pass through it to the load ?

 

Tags (1)
BillP
Administrator Administrator
Administrator
0 Likes
0
133

Re: Smart UPS & Smart UPS online

This reply was originally posted by Matt on APC forums on 1/9/2020


Hi Rico

 

If there is utility power to the UPS then it is functioning, the output can be switched off but the UPS will be on, so there isn't really a shutdown state when utility power is present.

 

Regards

 

Matt