Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79502members
344303posts

Smart-UPS SRT 5000 - Battery still charging

Solved
Acevirgil_apc
Cadet
0 Likes
1
157

Smart-UPS SRT 5000 - Battery still charging

This was originally posted on APC forums on 3/23/2017


Hello,

We have installed our Smart-UPS SRT 5000 7 days ago and it's up and running. I just want to ask why the battery shows still charging when checking the status on the web management? Is this normal?

Battery Charging

On the UPS unit display panel the battery charging symbol is not showing so it means battery is fully charged.

full charged

Firmware revision is UPS 04.0 (ID1013).

Thank you.

Attachments

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
157

Re: Smart-UPS SRT 5000 - Battery still charging

This reply was originally posted by Liam on APC forums on 3/24/2017


Hello - 

That is unusual. The load attached to the UPS is very small, which would likely cause the UPS to not be able to report efficiency, but I'm not sure why it would be saying "battery charging". If you look at the LCD screen, what does it report for efficiency? The UPS should usually say "N/A" on the LCD if there is not enough data for it to report accurately.

Liam

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
158

Re: Smart-UPS SRT 5000 - Battery still charging

This reply was originally posted by Liam on APC forums on 3/24/2017


Hello - 

That is unusual. The load attached to the UPS is very small, which would likely cause the UPS to not be able to report efficiency, but I'm not sure why it would be saying "battery charging". If you look at the LCD screen, what does it report for efficiency? The UPS should usually say "N/A" on the LCD if there is not enough data for it to report accurately.

Liam