Smart-UPS RT 8000 RM XL

Solved
henke_apc
Crewman
Crewman
0 Likes
2
78

Smart-UPS RT 8000 RM XL

This was originally posted on APC forums on 5/30/2013


We have two Smart-UPS RT 8000 RM XL that are both giving the following alarms.

Critical Alarm Replacement Battery Needed
At least one faulty battery exists.
  Critical Alarm Self-Test Failed
Self-Test Failed

What are the chances that both need to have batteries replaced?  Batteries are only about one year old..

Thanks

Tom


Accepted Solutions
henke_apc
Crewman
Crewman
0 Likes
0
78

Re: Smart-UPS RT 8000 RM XL

This was originally posted on APC forums on 5/30/2013


Did you program each UPS with the # of external battery modules?  I assumed these where internal batteries because they are in the UPS if that is incorrect, than it was not done and I would need to know how to do that.

See Answer In Context

2 Replies 2
henke_apc
Crewman
Crewman
0 Likes
0
78

Re: Smart-UPS RT 8000 RM XL

This was originally posted on APC forums on 5/30/2013


Each UPS has 4 batteries,  Current room temps for one ups is 84.99 F the other is 78.87 F.  I don't think a battery calibration has ever been done under a load.

henke_apc
Crewman
Crewman
0 Likes
0
79

Re: Smart-UPS RT 8000 RM XL

This was originally posted on APC forums on 5/30/2013


Did you program each UPS with the # of external battery modules?  I assumed these where internal batteries because they are in the UPS if that is incorrect, than it was not done and I would need to know how to do that.