Smart UPS RT 6000 + additional battery

Solved
keaton_apc
Crewman
Crewman
0 Likes
3
101

Smart UPS RT 6000 + additional battery

This was originally posted on APC forums on 5/22/2014


Hi everyone,

I have a Smart UPS RT 6000 and recently I bought an additional battery for it.

I connect the battery to the UPS but I think that it is not working yet, because for example the UPS was still 100% charged after I installed the battery.

I read somewhere (I think in the manual) that I have to "enable" the battery from the control panel of the UPS.

Ok, I went to the web browser interface of the UPS but I can't find any option to enable the battery or something like that..

Can someone tell what to do and where to "enable" the battery of the UPS?

Thx


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
101

Re: Smart UPS RT 6000 + additional battery

This reply was originally posted by Bill on APC forums on 5/23/2014


Hi,

The batteries are hot swappable so the UPS will not reboot / restart.

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
101

Re: Smart UPS RT 6000 + additional battery

This reply was originally posted by Angela on APC forums on 5/22/2014


In your Network Management Card, do you have a blue/white interface with tabs at the top?

If so, go to UPS->Configuration->General and you should have a field in there to add a number. It may say 1 already to count the internal battery so you can bump it to 2.

keaton_apc
Crewman
Crewman
0 Likes
0
101

Re: Smart UPS RT 6000 + additional battery

This was originally posted on APC forums on 5/23/2014


Ok I found it..just one more question: Does the UPS restart or do something that could disconnect the power supply to the servers attached to it?

BillP
Administrator Administrator
Administrator
0 Likes
0
102

Re: Smart UPS RT 6000 + additional battery

This reply was originally posted by Bill on APC forums on 5/23/2014


Hi,

The batteries are hot swappable so the UPS will not reboot / restart.