Posted: 2021-06-29 08:14 AM . Last Modified: 2024-03-12 03:12 AM
Hi
Kindly Help me as i had strange problem with my Smart UPS 700 and i tried to find solution or explanation, when i start my ups it came ON for about 2 minutes and get flashes continously with stopping of charging like in this video
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:14 AM . Last Modified: 2024-03-12 03:12 AM
No Tones at all...
I bought this ups used from a friend as we donot have APC agent in Egypt, he bought it from Italy
another problem when it work on battery i hear Rattle Sound and i opened the unit but i failed to determine the source of this rattle noise
thanks alot
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:14 AM . Last Modified: 2024-03-12 03:12 AM
Do you hear any tones with this condition (center 6 LEDs flashing)? This could be an Automatic Voltage Regulation (AVR) relay weld if no tone or a battery overvoltage if there is a tone.
Either way, it is typically not good and would likely require replacement or repair of something based on what region you're located in.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:14 AM . Last Modified: 2024-03-12 03:12 AM
No Tones at all...
I bought this ups used from a friend as we donot have APC agent in Egypt, he bought it from Italy
another problem when it work on battery i hear Rattle Sound and i opened the unit but i failed to determine the source of this rattle noise
thanks alot
Link copied. Please paste this link to share this article on your social media post.