Hello,
We have a Smart UPS 3000XL. Where is the Input circuit breaker located on this unit? There is an on/off switch on the power input - does this act as the breaker also?
Thank you,E
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:58 PM . Last Modified: 2 weeks ago
The switch right next to the input cord is the input circuit breaker for the UPS. You can verify because when the UPS is on and you flick this switch, the UPS stays on but goes to battery.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:58 PM . Last Modified: 2 weeks ago
The switch right next to the input cord is the input circuit breaker for the UPS. You can verify because when the UPS is on and you flick this switch, the UPS stays on but goes to battery.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:58 PM . Last Modified: 2 weeks ago
Thank you for the prompt response. This will assist in our troubleshooting.