Smart-UPS 3000 restarting after power loss

Solved
aandreyy_apc
Crewman
Crewman
0 Likes
5
202

Smart-UPS 3000 restarting after power loss

This was originally posted on APC forums on 2/27/2017


hi

looks like Smart-UPS 3000 we have restarting without any reason:

Event Log

 02/24/2017 09:14:09 UPS: The power for switched outlet group 1, Outlet Group 1, is now turned on.
 02/24/2017 09:14:09 UPS: The power for the main outlet group, UPS Outlets, is now turned on.
 02/24/2017 09:14:05 Environment: Restored the local network management interface-to-integrated Environmental Monitor (Universal I/O at Port 1) communication.
 02/24/2017 09:14:04 UPS: Restored the local network management interface-to-UPS communication.
 02/24/2017 09:13:54 System: Network service started. IPv6 address FE80::2C0:B7FF:FE5F:55D2 assigned by link-local autoconfiguration.
 02/24/2017 09:13:51 System: Network service started. System IP is 172.31.60.233 from manually configured settings.
 02/24/2017 09:13:35 System: Network Interface coldstarted.

 

UPS Network Management Card 2

Model:Smart-UPS 3000:Firmware Revision:UPS 06.5 / MCU 11.0 / UBL 08.2 / MBL 11.0 (ID18)Manufacture Date:12/09/2011 Apparent Power Rating:3000 VA

During testing after removing external power supply UPS restarted and after connecting external power supply UPS restarted.

Maybe you can advice what actions can be provided for future investigation?


Accepted Solutions
aandreyy_apc
Crewman
Crewman
0 Likes
0
202

Re: Smart-UPS 3000 restarting after power loss

This was originally posted on APC forums on 3/2/2017


just looked at old logs and can see that there was problem with battery detected earlier:

Event Log

02/20/2017 01:55:34 System: Network Interface coldstarted.
 02/18/2017 08:07:26 UPS: passed via internal operation a self-test.
 02/18/2017 08:07:16 UPS: Started a self-test.
 02/09/2017 19:15:06 System: NTP update successful.
 02/06/2017 01:35:48 UPS: passed via internal operation a self-test.
 02/06/2017 01:35:39 UPS: Started a self-test.
 02/04/2017 08:08:35 UPS: passed via internal operation a self-test.
 02/04/2017 08:08:27 UPS: Started a self-test.
 01/26/2017 19:14:52 System: NTP update successful.
 01/23/2017 01:15:57 UPS: passed via internal operation a self-test.
 01/23/2017 01:15:50 UPS: Started a self-test.
 01/23/2017 01:15:47 UPS: A faulty battery no longer exists.
 01/21/2017 08:09:39 UPS: passed via failed due to internal operation a self-test.
 01/21/2017 08:09:35 UPS: At least one faulty battery exists.
 01/21/2017 08:09:30 UPS: Started a self-test.
 01/12/2017 19:14:35 System: NTP update successful.
 01/09/2017 00:55:59 UPS: passed via internal operation a self-test.
 01/09/2017 00:55:49 UPS: Started a self-test.
 01/07/2017 08:10:57 UPS: passed via internal operation a self-test.
 01/07/2017 08:10:45 UPS: Started a self-test.
 12/29/2016 19:14:23 System: NTP update successful.
 12/26/2016 00:35:55 UPS: passed via internal operation a self-test.
 12/26/2016 00:35:45 UPS: Started a self-test.
 12/24/2016 08:12:06 UPS: passed via internal operation a self-test.
 12/24/2016 08:11:56 UPS: Started a self-test.
 12/15/2016 19:14:09 System: NTP update successful.
 12/12/2016 00:16:09 UPS: passed via internal operation a self-test.
 12/12/2016 00:15:58 UPS: Started a self-test.
 12/10/2016 08:13:19 UPS: passed via internal operation a self-test.
 12/10/2016 08:13:08 UPS: Started a self-test.
 12/06/2016 14:51:53 UPS: No longer on battery power.
 12/06/2016 14:51:52 UPS: On battery power in response to distorted input.
 12/06/2016 14:51:23 UPS: No longer on battery power.
 12/06/2016 14:51:22 UPS: On battery power in response to distorted input.
 12/01/2016 19:13:54 System: NTP update successful.
 11/27/2016 23:56:24 UPS: passed via internal operation a self-test.
 11/27/2016 23:56:13 UPS: Started a self-test.

but why it passes test now if battery is bad?

See Answer In Context

5 Replies 5
BillP
Administrator Administrator
Administrator
0 Likes
0
202

Re: Smart-UPS 3000 restarting after power loss

This reply was originally posted by Merick on APC forums on 2/27/2017


Hi Andrius

Sorry to hear you are having some issue with your unit, did the load attached to those outlets powered off?  Also I'd like to get the model number and serial number of the UPS.

Regards

aandreyy_apc
Crewman
Crewman
0 Likes
0
202

Re: Smart-UPS 3000 restarting after power loss

This was originally posted on APC forums on 2/27/2017


APC | UPS Network Management Card 2

Hi

About UPS
 
Model: Smart-UPS 3000
Serial Number: IS1150003308
Firmware Revision: UPS 06.5 / MCU 11.0 / UBL 08.2 / MBL 11.0 (ID18)
Manufacture Date: 12/09/2011
 
Apparent Power Rating: 3000 VA
Real Power Rating: 2700 W

during UPS restarts all equipment connected to UPS restarted. 

BillP
Administrator Administrator
Administrator
0 Likes
0
202

Re: Smart-UPS 3000 restarting after power loss

This reply was originally posted by Bill on APC forums on 3/1/2017


Hi,

It is possible that the battery needs to be replaced based on the age of the unit. Have you run a self-test and if so does it pass? Also, what is the battery voltage?

aandreyy_apc
Crewman
Crewman
0 Likes
0
202

Re: Smart-UPS 3000 restarting after power loss

This was originally posted on APC forums on 3/2/2017


hi

it can be battery, while i did not run self test but i can see in logs that before all outages there was performed self test authomatically:

Event Log

 02/20/2017 01:55:34 System: Network Interface coldstarted.
 02/18/2017 08:07:26 UPS: passed via internal operation a self-test.
 02/18/2017 08:07:16 UPS: Started a self-test.

does that can mean that battery in good condition? Also can provide output of UPS measurements and it also looks fine:

APC | UPS Network Management Card 2

Last Battery Transfer: None
Internal Temperature: 16.6°C
Runtime Remaining: 49min
UPS Input    
Input Voltage: 234.7 VAC @ 50.0 Hz
 
UPS Output  
Output Voltage: 234.7 VAC @ 50.0 Hz
Load Current: 3.1 Amps
 
Output VA: 23.4 %
Output Watts: 20.8 %
Output Efficiency: 98.0 %
Output Energy Usage: 22697.63 kWh
Battery Status  
Battery Capacity: 100.0 %
Battery Voltage: 54.8 VDC

aandreyy_apc
Crewman
Crewman
0 Likes
0
203

Re: Smart-UPS 3000 restarting after power loss

This was originally posted on APC forums on 3/2/2017


just looked at old logs and can see that there was problem with battery detected earlier:

Event Log

02/20/2017 01:55:34 System: Network Interface coldstarted.
 02/18/2017 08:07:26 UPS: passed via internal operation a self-test.
 02/18/2017 08:07:16 UPS: Started a self-test.
 02/09/2017 19:15:06 System: NTP update successful.
 02/06/2017 01:35:48 UPS: passed via internal operation a self-test.
 02/06/2017 01:35:39 UPS: Started a self-test.
 02/04/2017 08:08:35 UPS: passed via internal operation a self-test.
 02/04/2017 08:08:27 UPS: Started a self-test.
 01/26/2017 19:14:52 System: NTP update successful.
 01/23/2017 01:15:57 UPS: passed via internal operation a self-test.
 01/23/2017 01:15:50 UPS: Started a self-test.
 01/23/2017 01:15:47 UPS: A faulty battery no longer exists.
 01/21/2017 08:09:39 UPS: passed via failed due to internal operation a self-test.
 01/21/2017 08:09:35 UPS: At least one faulty battery exists.
 01/21/2017 08:09:30 UPS: Started a self-test.
 01/12/2017 19:14:35 System: NTP update successful.
 01/09/2017 00:55:59 UPS: passed via internal operation a self-test.
 01/09/2017 00:55:49 UPS: Started a self-test.
 01/07/2017 08:10:57 UPS: passed via internal operation a self-test.
 01/07/2017 08:10:45 UPS: Started a self-test.
 12/29/2016 19:14:23 System: NTP update successful.
 12/26/2016 00:35:55 UPS: passed via internal operation a self-test.
 12/26/2016 00:35:45 UPS: Started a self-test.
 12/24/2016 08:12:06 UPS: passed via internal operation a self-test.
 12/24/2016 08:11:56 UPS: Started a self-test.
 12/15/2016 19:14:09 System: NTP update successful.
 12/12/2016 00:16:09 UPS: passed via internal operation a self-test.
 12/12/2016 00:15:58 UPS: Started a self-test.
 12/10/2016 08:13:19 UPS: passed via internal operation a self-test.
 12/10/2016 08:13:08 UPS: Started a self-test.
 12/06/2016 14:51:53 UPS: No longer on battery power.
 12/06/2016 14:51:52 UPS: On battery power in response to distorted input.
 12/06/2016 14:51:23 UPS: No longer on battery power.
 12/06/2016 14:51:22 UPS: On battery power in response to distorted input.
 12/01/2016 19:13:54 System: NTP update successful.
 11/27/2016 23:56:24 UPS: passed via internal operation a self-test.
 11/27/2016 23:56:13 UPS: Started a self-test.

but why it passes test now if battery is bad?