I just purchased two used Smart-UPS 1400s, which utilize a serial connection. When I connect the serial cable to my server, then plug it into the UPS, it immediately kills the power to the UPS and thus, my server.
I assumed they use a standard db9 RS232 connection. Is that not right?
I tried this with and without having PowerChute installed. It made no difference.
When the serial cable was attached at both ends, I could not even turn the UPS on. I had to disconnect the cable from the UPS in order to power everything back up.
Any advice and insight would be much appreciated.
tia.
Posted: 2021-06-30 06:09 AM
This was originally posted on APC forums on 2/19/2008
Posted: 2021-06-30 06:09 AM
This reply was originally posted by Annie on APC forums on 2/17/2008
Hey,
You need to use the cable shipped with the UPS. Its part number should be 940-0024C or 940-0024D, or 940-1524C or 940-1524D , this depends on what specific UPS model you are using.
Posted: 2021-06-30 06:09 AM
This was originally posted on APC forums on 2/18/2008
Thanks for the reply.
As I purchased them used, they didn't come with cables. I'll see if I can find some.
Todd.