Smart-UPS 1000 apcupsd Problem

Solved
MAGIC_apc
Crewman
Crewman
0 Likes
2
214

Smart-UPS 1000 apcupsd Problem

This was originally posted on APC forums on 7/19/2016


Hi,

I ordered 2 Smart-UPS 1000 some weeks ago for some refugee project. But until now I had no net there, so I couldn't access the server via SSH and such.

Anyways, I installed the package today on the Ubuntu 16.04 server and changed the settings in order to accepting the USB cable as UPSTYPE.

But then I wanted to perform a selftest but nope, I will get following message

I don't know how to run a self test on your UPS
or your UPS does not support self test.

Did I miss something or does the UPS have no selftest? I am pretty sure, that some cheaper UPS from you have such option but this one doesnt

Regards


Accepted Solutions
MAGIC_apc
Crewman
Crewman
0 Likes
0
212

Re: Smart-UPS 1000 apcupsd Problem

This was originally posted on APC forums on 7/19/2016


Hi,

On 7/19/2016 10:13 PM, Bill said:

What is the exact model number of the Smart-UPS?

I will check it, when I visit the refugeehouse, so I hope on this weekend...

On 7/19/2016 10:13 PM, Bill said:

ny Smart-UPS that has a USB connection by default will run a self-test on start-up and every 14 days there after unless programmed not to. 

Yes, I know that since the Smart-UPS SUA750RMI1U I use for another house has such options in the SSH shell, and I can run the selftests whenever I want via the shell

Regards

 

PS:

I guess there's some other problem:

APC      : 001,018,0456
DATE     : 2016-07-19 20:53:36 +0000
HOSTNAME : HanS-Server
VERSION  : 3.14.12 (29 March 2014) debian
UPSNAME  : hans-server-8.og
CABLE    : USB Cable
DRIVER   : USB UPS Driver
UPSMODE  : Stand Alone
STARTTIME: 2016-07-19 20:53:26 +0000
STATUS   : COMMLOST
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME  : 0 Seconds
NUMXFERS : 0
TONBATT  : 0 Seconds
CUMONBATT: 0 Seconds
XOFFBATT : N/A
STATFLAG : 0x05000100
END APC  : 2016-07-19 21:01:36 +0000

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
212

Re: Smart-UPS 1000 apcupsd Problem

This reply was originally posted by Bill on APC forums on 7/19/2016


Peter,

What is the exact model number of the Smart-UPS?

You will find the information on the bar code sticker on the back of the unit.

Any Smart-UPS that has a USB connection by default will run a self-test on start-up and every 14 days there after unless programmed not to. 

Attachments
MAGIC_apc
Crewman
Crewman
0 Likes
0
213

Re: Smart-UPS 1000 apcupsd Problem

This was originally posted on APC forums on 7/19/2016


Hi,

On 7/19/2016 10:13 PM, Bill said:

What is the exact model number of the Smart-UPS?

I will check it, when I visit the refugeehouse, so I hope on this weekend...

On 7/19/2016 10:13 PM, Bill said:

ny Smart-UPS that has a USB connection by default will run a self-test on start-up and every 14 days there after unless programmed not to. 

Yes, I know that since the Smart-UPS SUA750RMI1U I use for another house has such options in the SSH shell, and I can run the selftests whenever I want via the shell

Regards

 

PS:

I guess there's some other problem:

APC      : 001,018,0456
DATE     : 2016-07-19 20:53:36 +0000
HOSTNAME : HanS-Server
VERSION  : 3.14.12 (29 March 2014) debian
UPSNAME  : hans-server-8.og
CABLE    : USB Cable
DRIVER   : USB UPS Driver
UPSMODE  : Stand Alone
STARTTIME: 2016-07-19 20:53:26 +0000
STATUS   : COMMLOST
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME  : 0 Seconds
NUMXFERS : 0
TONBATT  : 0 Seconds
CUMONBATT: 0 Seconds
XOFFBATT : N/A
STATFLAG : 0x05000100
END APC  : 2016-07-19 21:01:36 +0000