Short Story: We want the UPS to shutdown at 30 minutes (run time currently 1 hour 16 mins) to make sure space does not overheat. We do not use PowerChute.
Symmetra 8K (Mfg date: 12/2/2009) with equipment that cannot be controlled with PowerChute.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:55 AM . Last Modified: 2024-03-07 10:24 PM
Hi,
If you upgrade the NMC to a AP9630 or AP9631 you will have the options that Matt suggested.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:55 AM . Last Modified: 2024-03-07 10:25 PM
Hi Don
Which NMC do you have installed in the Symmetra? The manufacture date is around the time that the 2nd Generation NMCs came out and they have the below section for on the shutdown page, which has settings that are not present on the AP9619.
Regards
Matt
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:55 AM . Last Modified: 2024-03-07 10:24 PM
Hi,
If you upgrade the NMC to a AP9630 or AP9631 you will have the options that Matt suggested.