Posted: 2021-07-08 12:45 AM
This was originally posted on APC forums on 6/18/2015
Hi,
I have various Smart UPS's installed at clients, ive been sold to that these UPS's, can issue a clean shutdown command to the servers thru powerchute, then the servers shutdown all OK.
Then when the power is restored after sometime, even after the UPS is drained flat.. It will then start the server up, i cannot seem to get this to work. I believe its actually impossible.
How does the APC issue a command to an off server to startup.
Can anyone shed some light on this?
Thanks in advnace.
Posted: 2021-07-08 12:46 AM
This was originally posted on APC forums on 6/19/2015
There should be a BIOS setting to turn the computer back on after a power outage. There's a picture here:
http://www.servethehome.com/keeping-servers-bios-setup-availibility/
Posted: 2021-07-08 12:46 AM
This reply was originally posted by Bill on APC forums on 6/18/2015
Craig,
the UPS cannot issue a power on command that is done through the BIOS of the computer. See Kbase FA159547.
Posted: 2021-07-08 12:46 AM
This was originally posted on APC forums on 6/18/2015
Thanks Bill,
will the BIOS setting assist even if powerchute has told the server to shutdown?
Posted: 2021-07-08 12:46 AM
This reply was originally posted by Bill on APC forums on 6/18/2015
Craig,
Yes. If set up properly configured when PowerChute commands the OS down the UPS will wait a defined amount of time than then kill power to the outlets. When AC is restored the UPS will restore power to the outlets which in turn causes the computer to start up.
Posted: 2021-07-08 12:46 AM
This was originally posted on APC forums on 6/19/2015
There should be a BIOS setting to turn the computer back on after a power outage. There's a picture here:
http://www.servethehome.com/keeping-servers-bios-setup-availibility/