Can i Sync SUVTP30KVA with SUVTP40kVA in parallel & Redundant configuration. as both of them have same frame size and other utilities.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:09 PM . Last Modified: 2024-03-06 11:22 PM
Ali,
I verified with the 3 Phase power team that both UPS must be the same. You cannot mix a SUVTP40 with a SUVTP30.