SURTD5000XLI not working, no lights

Solved
SchoolTechMill_apc
Crewman
Crewman
0 Likes
3
87

SURTD5000XLI not working, no lights

This was originally posted on APC forums on 4/26/2017


Hi,

After a power outage yesterday, our SURTD5000XLI will not power up, nor power the servers connected to it.

The batteries are known to be bad, and I have a new set in order processing currently. I did read that the batteries need 80VA for it to turn on, and I suspect that is the issue.

However, I have taken out the Network Management Card 2, and put it into another UPS, and there does not seem to be any events in the log regarding the power outage at all. It has gone from complaining about the batteries a few days ago, to powering up once I put the card in the other UPS. Is this expected? Or is there a good chance the UPS is dead and needs replacing? The unit is 5-6 years old, but budget is tight so trying not to make expensive rash decisions!

Thanks


Accepted Solutions
SchoolTechMill_apc
Crewman
Crewman
0 Likes
0
87

Re: SURTD5000XLI not working, no lights

This was originally posted on APC forums on 4/27/2017


Thank you both, that is my feeling also. I will have to ask the director if they want to risk spending £340 on a new set of batteries with no guarantee that it will work!

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
87

Re: SURTD5000XLI not working, no lights

This reply was originally posted by Liam on APC forums on 4/26/2017


Hello - 

If possible I would recommend checking the voltage of the battery packs with a voltmeter. If they are under 80v at all it is very likely that the batteries just need to be replaced. If they are also 5-6 years old and original to the UPS, it would make sense that they have failed. Average life span of a battery module in this unit is 3-5 years.

UnexpectedBill_apc
Captain
Captain
0 Likes
0
87

Re: SURTD5000XLI not working, no lights

This was originally posted on APC forums on 4/26/2017


You should be on the right track. These units, and similar models, won't power up without a good set of batteries in place.

If the batteries were bad enough, it's possible that the NMC2 lost power before it could log an event concerning the power outage.

SchoolTechMill_apc
Crewman
Crewman
0 Likes
0
88

Re: SURTD5000XLI not working, no lights

This was originally posted on APC forums on 4/27/2017


Thank you both, that is my feeling also. I will have to ask the director if they want to risk spending £340 on a new set of batteries with no guarantee that it will work!