SURT8000 UPS network card

This was originally posted on APC forums on 8/31/2012


Hello I have a SURT8000 UPS device that I need to configure the built in network card.

As with the 1500 devices you need to reboot the network card when you build the configuration and I am not even sure if it reboots those UPS's

my question is do i have to reboot the network card in the 8000's and will it turn the entire UPS off and back on when I do it?

Thanks!

Adam


Accepted Solutions
voidstar_apc
Janeway
Janeway
0 Likes
0
64

Re: SURT8000 UPS network card

This was originally posted on APC forums on 8/31/2012


Rebooting the network management card (NMC) does not reboot the UPS. And yes, some configuration changes on the NMC do require rebooting the NMC (but not the UPS).

See Answer In Context

1 Reply 1
voidstar_apc
Janeway
Janeway
0 Likes
0
65

Re: SURT8000 UPS network card

This was originally posted on APC forums on 8/31/2012


Rebooting the network management card (NMC) does not reboot the UPS. And yes, some configuration changes on the NMC do require rebooting the NMC (but not the UPS).