Currently have a total of five SURT192XLBP battery packs connected to a production/online SURT10000XLT and I would like to uninstall three of them. Can this be done while leaving the system online and loaded?
Thanks,
-Ben
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-27 11:36 PM . Last Modified: 2024-03-19 12:03 AM
Hi Ben,
Yes, there is no problem in doing that. You'll just be unplugging the DC connectors which will not disrupt the UPS operation.