SURT192XLBP: hot uninstall?

Solved
bminehart_apc
Cadet
0 Likes
1
100

SURT192XLBP: hot uninstall?

This was originally posted on APC forums on 2/10/2015


Currently have a total of five SURT192XLBP battery packs connected to a production/online SURT10000XLT and I would like to uninstall three of them. Can this be done while leaving the system online and loaded?

Thanks,

-Ben


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
100

Re: SURT192XLBP: hot uninstall?

This reply was originally posted by Angela on APC forums on 2/11/2015


Hi Ben,

Yes, there is no problem in doing that. You'll just be unplugging the DC connectors which will not disrupt the UPS operation.

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
101

Re: SURT192XLBP: hot uninstall?

This reply was originally posted by Angela on APC forums on 2/11/2015


Hi Ben,

Yes, there is no problem in doing that. You'll just be unplugging the DC connectors which will not disrupt the UPS operation.