Posted: 2021-07-07 11:22 PM
This question was originally posted by Stewart on APC forums on 8/4/2015
Hi Folks,
Wondering if there's a minimum input current for the SURT 8000VA?
Thanks.
Posted: 2021-07-07 11:22 PM
This reply was originally posted by Angela on APC forums on 8/4/2015
You're welcome. So the product page is here -> http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SURT8000RMXLI
The answer appears to be a minimum input of 160V for the UPS to operate at a full load. I also double checked some technical specifications which said:
Posted: 2021-07-07 11:22 PM
This reply was originally posted by Angela on APC forums on 8/4/2015
Can you clarify the model? SURT8000XLT or SURT8000XLI?
Usually there is no minimum current but rather a minimum input voltage to operate. Depending on the model, we can find that out for you.
Posted: 2021-07-07 11:22 PM
This reply was originally posted by Stewart on APC forums on 8/4/2015
Hi Angela,
Thanks for the quick response. It's an 8000RMXLI.
Posted: 2021-07-07 11:22 PM
This reply was originally posted by Angela on APC forums on 8/4/2015
You're welcome. So the product page is here -> http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SURT8000RMXLI
The answer appears to be a minimum input of 160V for the UPS to operate at a full load. I also double checked some technical specifications which said: