SURT 8000VA RM 230V Minimum input current

This question was originally posted by Stewart on APC forums on 8/4/2015


Hi Folks,

Wondering if there's a minimum input current for the SURT 8000VA?

Thanks.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
77

Re: SURT 8000VA RM 230V Minimum input current

This reply was originally posted by Angela on APC forums on 8/4/2015


You're welcome. So the product page is here -> http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SURT8000RMXLI 

The answer appears to be a minimum input of 160V for the UPS to operate at a full load. I also double checked some technical specifications which said:

  • Input voltage range at full load 160 to 280VAC
  • Input voltage range at half load 100 to 280VAC

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
77

Re: SURT 8000VA RM 230V Minimum input current

This reply was originally posted by Angela on APC forums on 8/4/2015


Can you clarify the model? SURT8000XLT or SURT8000XLI?

Usually there is no minimum current but rather a minimum input voltage to operate. Depending on the model, we can find that out for you.

BillP
Administrator Administrator
Administrator
0 Likes
0
77

Re: SURT 8000VA RM 230V Minimum input current

This reply was originally posted by Stewart on APC forums on 8/4/2015


Hi Angela,

Thanks for the quick response. It's an 8000RMXLI.

BillP
Administrator Administrator
Administrator
0 Likes
0
78

Re: SURT 8000VA RM 230V Minimum input current

This reply was originally posted by Angela on APC forums on 8/4/2015


You're welcome. So the product page is here -> http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SURT8000RMXLI 

The answer appears to be a minimum input of 160V for the UPS to operate at a full load. I also double checked some technical specifications which said:

  • Input voltage range at full load 160 to 280VAC
  • Input voltage range at half load 100 to 280VAC