Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
You can subscribe to this forum after you log in or create your free account..
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
Posted: 2021-06-30 02:28 AM
This was originally posted on APC forums on 5/6/2011
I have this UPS that I am pretty sure has never been used and setting in a box in my storage for the last 4 years. When connected to power it is one continuous beep, per the manual indicating a fault(fault light is on too). Also the battery fail light comes on. I still get the fault with the battery module unplugged.
What I would like to know will the failed battery produce the fault like this or is it something else. I know most ups's will fault on bad or no battery. I just need to know if this is likely what the issue is before i spend money to purchase new batteries.
Thanks in advance for any input.
Posted: 2021-06-30 02:28 AM
This was originally posted on APC forums on 5/6/2011
Actually i just found some new batteries and installed them. No more battery light but i still get a continous beep, the unit seems to otherwise work. No wiring faults..
Posted: 2021-06-30 02:28 AM
This reply was originally posted by Jonathan on APC forums on 5/6/2011
Good day Joe,
A flashing replace battery indicator means that the internal battery is not connected or the UPS fails to detect the battery. Is there any pattern with the beep? Are there any LED's lit on the UPS?
Posted: 2021-06-30 02:28 AM
This reply was originally posted by Bernard on APC forums on 5/8/2011
Hi Joe
If the unit is chirping and the Replace Battery Indicator is flashing and the unit is chirping, it means that the battery is not connected, it could be because the battery is discharged or the unit itself is not seeing the batteries you have installed. If the unit emits a constant tone and but all the LEDs in the front of the unit seem to be normal and the unit still has that constant tone, it may indicated an internal failure. I suggest that you get in touch with technical support at 1 800 800 4272.
I hope this helps
User | Count |
---|---|
4834 | |
190 | |
111 | |
108 | |
67 | |
63 |
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.