Hi, I bought a used SUA1500RM2U that came with the AP9617 management card. I read in the manual that i need a APC serial cable to connect to PC to reset the AP9617. I bought a new cable off ebay APC 940-0020C.
I hooked up the serial and set my only serial port to 2400-8-N-1-N COM1 in windows
I used putty and set it to the same serial speed above.
pressed enter in putty, nothing on the screen.
tried different speeds 9600-8-N-1-N
reconnect with putty, no output on screen.
then i tried to do the reset procedure anyways.
pressed and released the reset button on AP9617 card, LED flash quickly, I pressed and released the reset button again.
i then pressed my enter button continuously until the LED stop flashing and remained steady pressed some more.
Still no prompt on my PUTTY.
I then removed the AP9617 card out of the UPS think it may be defective.
try connecting serial with putty again, nothing on screen.
then i removed the battery from the AP9617 and left it alone for a week, hoping it would lose it settings, but still nothing.
any help is appreciated, or do i have a defective serial port an/or AP9617?
BTW, when I plug the UPS using the USB cable to my UNRAID server, it reads everything about the UPS no problem.
I just want to try to get the AP9617 card working
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 06:02 AM . Last Modified: 2024-02-15 12:10 AM
Hi,
You need smart signalling cable 940-0024. Cable 940-0020 is simple signalling meaning it is one way communications. From UPS to computer. The smart signalling cable is two way.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 06:01 AM . Last Modified: 2024-02-15 12:10 AM
I believe on that UPS using USB disables the serial port. To re-enable the serial port, unplug the UPS and its battery, wait for a few seconds for the fan to stop spinning and the lights to go out, and then re-assemble the unit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 06:02 AM . Last Modified: 2024-02-15 12:10 AM
Hi,
You need smart signalling cable 940-0024. Cable 940-0020 is simple signalling meaning it is one way communications. From UPS to computer. The smart signalling cable is two way.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.