SUA1000uxi + new battery pack

This was originally posted on APC forums on 5/1/2013


we have installed a new 24v 60ah battery pack to SUA1000uxi ups

right now @30% load the backup time is 3 hours

still the Battery level indicator is always flashing low battery

please let me have solution to fix the "Battery Level Indicator"

Tags (3)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
54

Re: SUA1000uxi + new battery pack

This reply was originally posted by Angela on APC forums on 5/3/2013


  1. are these APC battery packs or third party?
  2. Do you have any software or network management card installed with this UPS that allows you to update the battery pack count? Or has that already been set?
  3. Can you verify the icon near the low battery indicator you are seeing? Because there is a battery with an X through it or a battery charge graph with five LEDs and these icons can mean different things.

This model UPS requires you to tell it how many battery packs are attached to account for more accurate runtime. If this count is already updated, then let me know what it is set to and what led to adding this battery pack (did you replace failing batteries or add this on new, etc).

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
55

Re: SUA1000uxi + new battery pack

This reply was originally posted by Angela on APC forums on 5/3/2013


  1. are these APC battery packs or third party?
  2. Do you have any software or network management card installed with this UPS that allows you to update the battery pack count? Or has that already been set?
  3. Can you verify the icon near the low battery indicator you are seeing? Because there is a battery with an X through it or a battery charge graph with five LEDs and these icons can mean different things.

This model UPS requires you to tell it how many battery packs are attached to account for more accurate runtime. If this count is already updated, then let me know what it is set to and what led to adding this battery pack (did you replace failing batteries or add this on new, etc).