APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:13 PM . Last Modified: 3 weeks ago
There is SRT8KRMXLI (ID1014) with AP9537SUM. AOS/SMUX version is 6.4.0 (the latest), UPS firmware version is 04.4 (also the latest).
1. There is no option "Last Battery Replacement" in the web interface. (I use CLI commands "detbat -id 1 1" and "detbat -id 1 2" as workaround.)
2. There is no option "External Batteries". At this time we have no external batteries, but will this option appear when we connect a battery? Or this option is not needed with new (SRT* / SMX*) models?
3. I can't set "Battery Health Alarm Warning Time" and "Battery Health Alarm Sleep Time" to "-1". Web interface says "Battery Health Alarm Warning Time (-1) has been entered incorrectly. / Battery Health Alarm Sleep Time (-1) has been entered incorrectly." Is it a bug or a feature? How to disable notification warning?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:13 PM . Last Modified: 3 weeks ago
Hi,
On 5/30/2016 3:17 AM, Andrej said:1. There is no option "Last Battery Replacement" in the web interface. (I use CLI commands "detbat -id 1 1" and "detbat -id 1 2" as workaround.)
Go to Status and select Battery System, the select the Battery pack to set the replacement date.
On 5/30/2016 3:17 AM, Andrej said:2. There is no option "External Batteries". At this time we have no external batteries, but will this option appear when we connect a battery? Or this option is not needed with new (SRT* / SMX*) models?
Yes. When adding a battery pack it will appear in Battery System.
On 5/30/2016 3:17 AM, Andrej said:3. I can't set "Battery Health Alarm Warning Time" and "Battery Health Alarm Sleep Time" to "-1". Web interface says "Battery Health Alarm Warning Time (-1) has been entered incorrectly. / Battery Health Alarm Sleep Time (-1) has been entered incorrectly." Is it a bug or a feature? How to disable notification warning?
This issue is under review and will be address in a future firmware release.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:13 PM . Last Modified: 3 weeks ago
Hi,
On 5/30/2016 3:17 AM, Andrej said:1. There is no option "Last Battery Replacement" in the web interface. (I use CLI commands "detbat -id 1 1" and "detbat -id 1 2" as workaround.)
Go to Status and select Battery System, the select the Battery pack to set the replacement date.
On 5/30/2016 3:17 AM, Andrej said:2. There is no option "External Batteries". At this time we have no external batteries, but will this option appear when we connect a battery? Or this option is not needed with new (SRT* / SMX*) models?
Yes. When adding a battery pack it will appear in Battery System.
On 5/30/2016 3:17 AM, Andrej said:3. I can't set "Battery Health Alarm Warning Time" and "Battery Health Alarm Sleep Time" to "-1". Web interface says "Battery Health Alarm Warning Time (-1) has been entered incorrectly. / Battery Health Alarm Sleep Time (-1) has been entered incorrectly." Is it a bug or a feature? How to disable notification warning?
This issue is under review and will be address in a future firmware release.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 10:13 PM . Last Modified: 3 weeks ago
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.