APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:08 AM . Last Modified: 2024-03-18 02:43 AM
Hello,
i have two SRT 2200 XLI, and both have the the same failure "charger low voltage" event code 142.
both have been repaired due to fan failures within 4 month.
when i got them back one started directly with mentioned error. but was just once a day now both UPS's have the same error plugged or on plugged in the wall. one error after the other, all event code 142
i looked around but couldn't find event code 142.
is this a setting i can adjust or is the charger toast and need to be replaced ?
batteries are still good indicated by the ups
thanks in advance
Arjen Hoekman
Lima
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:08 AM . Last Modified: 2024-03-18 02:43 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:08 AM . Last Modified: 2024-03-18 02:43 AM
Hello -
This event usually indicates a blown fuse in the charger of the UPS. I would suggest contacting your local technical support group for further assistance and/or getting a replacement unit under warranty. This fuse is not field serviceable.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:08 AM . Last Modified: 2024-03-18 02:43 AM
thanks Liam, ill contact the local team
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.