Posted: 2022-05-19 08:54 AM
SRT 3000
Date : 05/18/2022
Time : 14:38:48
Code : 0x011B
Critical - UPS: In bypass in response to an internal hardware fault.
Then one second later
Date : 05/18/2022
Time : 14:38:49
Code : 0x01B2
Informational - UPS: Return from bypass, internal hardware fault no longer present.
Random times in the day.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-05-19 09:55 PM
Hi
I am curious is the firmware upgrade you mentioned is of the UPS itself or the network card?
If it is the latter, I would suggest trying a downgrade and check if the fault still appears.
Just to identify if the issue is rooted in malfunctioning hardware or a software issue.
You can find the 2.0 version of the firmware here:
I would suggest using the FTP or SCP process for the downgrade, as detailed in this document.
-> https://www.apc.com/ie/en/faqs/index?page=content&id=FA156047
If the issue is still present after the downgrade, I would advice getting the support file from the network card and contact your local customer care center.
https://www.apc.com/us/en/support/contact-us/ (for local info change the country as appropiate)
Best regards
Tonny
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-05-23 11:06 AM
Downgrading the AP9640 network card from 2.2.0.1 to 2.0.0.5 fixed the issue.
Thanks,