Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
You can subscribe to this forum after you log in or create your free account..
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
Posted: 2021-06-30 09:43 PM
This was originally posted on APC forums on 8/24/2016
I have been trying to monitor a group of UPSs using nagios.
SNMP works more or less if line power is off or output off, but determining battery health seems broken.
But if I query OID 1.3.6.1.4.1.318.1.1.1.2.2.4.0, it always returns "1" regardless if the battery is plugged in or whether the battery is unplugged and the "replace battery" indicator is on and beeping.
I unplugged the battery to simulate a bad one.
Is the SNMP MIB broken? I have tried two different 750 units with same results.
Posted: 2021-06-30 09:43 PM
This reply was originally posted by Angela on APC forums on 8/26/2016
Hi Tim,
Okay, thanks for the info. I expect the OID to work just as you expect. But, I also think what you're simulating is "battery disconnected" rather than battery needs replacing. That is why I suggested to check what the other interfaces report as the current alarm when you try disconnecting the battery. You'd need to have a self test that fails to get a replace battery indicator or replace battery message.
I am not sure if this will work and I can't try it today myself but you could try disconnecting the battery and then also running a self test afterwards to see if it triggers a replace battery and re-check the OIDs. I am not sure the UPS will refuse the self test because there is no battery or if it may trigger a self test failed. Depending on the UPS model, they also may act a little differently. I also cannot be sure without trying if the UPS will turn off so I'd proceed with a non-critical load if possible, especially if you force a self test through the UPS display versus issuing a self test command from the management interface or SNMP OID. Typically, UPS logic will come into play if you issue the command but using the front panel LCD will force a self test so in this scenario I'd be cautious of forcing a self test through the front panel as I am not sure if the UPS will force a self test still with no battery and then turn off. I can try this Monday if you prefer to wait for me. I have an SUA and SMT.
As a side note which may come into play later, 6.4.0 is the latest firmware version available for Smart-UPS with AP9630/31/35. Not sure if you want to upgrade (lots of security fixes) but we may need to give it a try if in the future we still see a problem when truly triggering a replace battery condition AKA failed self test.
Posted: 2021-06-30 09:43 PM
This was originally posted on APC forums on 8/24/2016
Also strangely, the OID querty for .1.3.6.1.4.1.318.1.1.1.2.2.1.0 ("upsAdvBatteryCapacity.0") reads 47 even with the battery unplugged...
Posted: 2021-06-30 09:43 PM
This reply was originally posted by Angela on APC forums on 8/24/2016
Hi Tim,
Can you give me an exact model of the Smart-UPS 750? A response to .1.3.6.1.4.1.318.1.1.1.1.2.5 or .1.3.6.1.4.1.318.1.1.1.1.1.1 would be good.
Also, can you check the other interfaces beyond SNMP like web, telnet/ssh or local serial interfaces and let me know if the Network Management Card is reporting a correct status there?
Lastly, the sysDescr (.1.3.6.1.2.1.1.1) could be useful too to tell me what firmware you have on your UPS Network Management Card.
Posted: 2021-06-30 09:43 PM
This was originally posted on APC forums on 8/24/2016
Models SUA750 and SMT750. Also tried a SMT1500, all same results, 1.3.6.1.4.1.318.1.1.1.2.2.4.0 doesn't change if battery is disconnected either by removing or disconnecting the jumper.
I have many other SNMP OIDs reporting as expected on these units, like input voltage, output voltage, % charge, battery temp, etc.
I was trying to test my Nagios monitor to make sure it would warn us if the battery were bad, maybe I can't unplug the battery it to simulate a bad battery.
I was thinking that the "replace battery" LED could be detected through an SNMP query, based on this from the Powernet MIB description:
APC UPS :: Replace Battery
Monitor Type SNMP - QA Monitor
SNMP Object Type upsAdvBatteryReplaceIndicator
OID 1.3.6.1.4.1.318.1.1.1.2.2.4.0
Returns Indicates whether the UPS batteries need to be replaced:
1 = Batteries do not need replacing
2 = Batteries need replacing
Monitoring Condition Pass if not equal to 2
Monitor failure indicates that there is a UPS battery that needs to be changed. The UPS may not perform as desired should a power failure occur.
However, I'm not sure this value is really the same thing as the "replace battery" indicator LED on the front of the unit...
Posted: 2021-06-30 09:43 PM
This was originally posted on APC forums on 8/25/2016
About the card, OID 1.3.6.1.2.1.1.0 reports:
MB:v4.1.0 PF:v6.2.1 PN:apc_hw05_aos_621.bin AF1:v6.2.1 AN1:apc_hw05_sumx_621.bin MN:AP9631 HR:08
Posted: 2021-06-30 09:43 PM
This reply was originally posted by Angela on APC forums on 8/26/2016
Hi Tim,
Okay, thanks for the info. I expect the OID to work just as you expect. But, I also think what you're simulating is "battery disconnected" rather than battery needs replacing. That is why I suggested to check what the other interfaces report as the current alarm when you try disconnecting the battery. You'd need to have a self test that fails to get a replace battery indicator or replace battery message.
I am not sure if this will work and I can't try it today myself but you could try disconnecting the battery and then also running a self test afterwards to see if it triggers a replace battery and re-check the OIDs. I am not sure the UPS will refuse the self test because there is no battery or if it may trigger a self test failed. Depending on the UPS model, they also may act a little differently. I also cannot be sure without trying if the UPS will turn off so I'd proceed with a non-critical load if possible, especially if you force a self test through the UPS display versus issuing a self test command from the management interface or SNMP OID. Typically, UPS logic will come into play if you issue the command but using the front panel LCD will force a self test so in this scenario I'd be cautious of forcing a self test through the front panel as I am not sure if the UPS will force a self test still with no battery and then turn off. I can try this Monday if you prefer to wait for me. I have an SUA and SMT.
As a side note which may come into play later, 6.4.0 is the latest firmware version available for Smart-UPS with AP9630/31/35. Not sure if you want to upgrade (lots of security fixes) but we may need to give it a try if in the future we still see a problem when truly triggering a replace battery condition AKA failed self test.
User | Count |
---|---|
4834 | |
190 | |
111 | |
108 | |
67 | |
63 |
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.