SMX1500RM2U Strange Behavior

Solved
gendoikari_apc
Crewman
Crewman
0 Likes
7
195

SMX1500RM2U Strange Behavior

This was originally posted on APC forums on 9/13/2013


I just got my SMX1500RM2U on Tuesday, Sept 10th, and charged it for a good twelve hours, even thou it seemed to have a full battery. Then I mounted it and have been using it with my computer. Then about the next day I noticed it had recorded two power failures.

And then about Wednesday night, I noticed it kept clicking, and had recorded 118 power failures. None of my other UPS units had switched on, and even computers I had plugged into the wall were still on and running. I then switched the power sensitivity settings form normal to reduced, and that seemed to stop it from clicking so much.

Well I woke up today to constant clicking, the battery down to 54%, and the SMX1500RM2U kept switching from wall power to battery (green>orange>green>orange led). Well I tried unplugging it, which switched it to battery and stopped the constant clicking, but their seemed to be a delay in it detecting whether it was plugged into the wall or not. I switched outlets, even tried plugging it into one of the surge ports of another UPS in case my wall power or the outlets were somehow bad. I then had to quickly shut down my machine, and luckily it still works, boots into windows, and I have backups.

As i said, i shut down my machine, unplugged everything from the SMX1500RM2U, and ran the self-diagnostic, which came back fine, but it was still constantly clicking and switching between the wall outlet and the battery. Now I have the power sensitivity set to low, and everything seems fine, but is my unit slowly failing?

Tags (2)

Accepted Solutions
gendoikari_apc
Crewman
Crewman
0 Likes
0
196

Re: SMX1500RM2U Strange Behavior

This was originally posted on APC forums on 9/20/2013


Ahh, I see the advanced editor option now, sorry about that!

Anyhow, I set the sensitivity to low, and not a peep out of the SMX1500RM2U. I'm a bit worried that it may be letting more "noise" through, thou I wouldn't know how to tell. This also is a relief as I was planning on buying a second SMX1500RM2U, and now know what settings to use. Thank you for your time. =3

See Answer In Context

7 Replies 7
BillP
Administrator Administrator
Administrator
0 Likes
0
197

Re: SMX1500RM2U Strange Behavior

This reply was originally posted by Angela on APC forums on 9/13/2013


Can you tell me under the About menu on the front LCD of the UPS what you see for firmware versions on the UPS?

Also, does the UPS have PowerChute or a UPS Network Management Card (NMC) installed? If so, I'd be interested in the logs from those.

You could also find the firmware through PowerChute or an NMC.

It sounds like a hysteresis problem off the top of my head. A self test only tests the on battery operation of the unit and not anything else.

gendoikari_apc
Crewman
Crewman
0 Likes
0
197

Re: SMX1500RM2U Strange Behavior

This was originally posted on APC forums on 9/13/2013


It only shows one firmware version,  UPS 09.1 / MCU 09.1 (20 - 5).

And I have no NMC card installed, but I do have PowerChute business edition.

And I'm not sure how to post the logs I here. I can export the event log, but I don't see an option for the data log?

BillP
Administrator Administrator
Administrator
0 Likes
0
197

Re: SMX1500RM2U Strange Behavior

This reply was originally posted by Angela on APC forums on 9/13/2013


PowerChute won't let you easily export the data log, just the event as you've found. I'll take the event and any screenshots of the data log you feel like providing just so I can see what it logs during some of these transfers.

On this unit there is also line quality as a setting I think too, correct? Just wanted to know if you also have adjusted that in conjunction with the sensitivity.

In the meantime, I will do some additional asking around about this type of issue for anything else we should be checking or doing. There is a firmware update for this UPS but I don't see anything like this type of symptom this on there as a bug fix. Here are the release notes for UPS 09.2 just as an FYI.

  • Added improved bootloader to protect against malicious attacks
  • Improved the fault log display of errors.
  • Changed the default value for LowRuntimeWarning to 150s
  • Improved the efficiency display to indicate reason for low efficiency

gendoikari_apc
Crewman
Crewman
0 Likes
0
197

Re: SMX1500RM2U Strange Behavior

This was originally posted on APC forums on 9/13/2013


Alright, I screen capped the data log.

1423_Upsdatalog01.jpg1424_Upsdatalog02.jpg1425_Upsdatalog03.jpg1426_Upsdatalog04.jpg1427_Upsdatalog05.jpg1428_Upsdatalog06.jpg

gendoikari_apc
Crewman
Crewman
0 Likes
0
197

Re: SMX1500RM2U Strange Behavior

This was originally posted on APC forums on 9/13/2013


And here is the event log. I'd rather be able to have it as an attachment, but that doesn't seem to be an option on this forum.

9/10/13 18:53:08 Monitoring Started

9/10/13 18:53:10 Communication Established

9/10/13 18:53:11 Online (Green Mode) - Entered

9/10/13 18:53:13 To ensure safe OS shutdown, TurnOff delay for Outlet Group 1 was adjusted to 180 seconds 

9/10/13 19:22:04 AVR Boost Active

9/10/13 19:22:07 AVR Boost No Longer Active

9/10/13 21:53:49 Online (Green Mode) - Exited

9/10/13 21:53:49 Power Failed

9/10/13 21:53:50 Power Restored

9/10/13 21:53:50 Online (Green Mode) - Entered

9/11/13 01:10:40 Online (Green Mode) - Exited

9/11/13 01:10:41 Online (Green Mode) - Entered

9/11/13 05:53:08 Online (Green Mode) - Exited

9/11/13 05:53:08 Power Failed

9/11/13 05:53:09 Power Restored

9/11/13 05:53:09 Online (Green Mode) - Entered

9/12/13 02:53:07 Online (Green Mode) - Exited

9/12/13 02:53:07 Power Failed

9/12/13 02:53:08 Power Restored

9/12/13 02:53:08 Online (Green Mode) - Entered

9/12/13 06:53:31 Online (Green Mode) - Exited

9/12/13 06:53:31 Power Failed

9/12/13 06:53:32 Power Restored

9/12/13 06:53:32 Online (Green Mode) - Entered

9/12/13 07:12:01 Online (Green Mode) - Exited

9/12/13 07:12:01 Power Failed

9/12/13 07:12:02 Power Restored

9/12/13 07:12:02 Online (Green Mode) - Entered

9/12/13 07:12:05 Online (Green Mode) - Exited

9/12/13 07:12:05 Power Failed

9/12/13 07:12:06 Power Restored

9/12/13 07:12:06 Online (Green Mode) - Entered

9/12/13 07:12:09 Online (Green Mode) - Exited

9/12/13 07:12:09 Power Failed

9/12/13 07:12:10 Power Restored

9/12/13 07:12:10 Online (Green Mode) - Entered

9/12/13 07:12:15 Online (Green Mode) - Exited

9/12/13 07:12:15 Power Failed

9/12/13 07:12:16 Power Restored

9/12/13 07:12:16 Online (Green Mode) - Entered

9/12/13 07:12:19 Online (Green Mode) - Exited

9/12/13 07:12:19 Power Failed

9/12/13 07:12:20 Power Restored

9/12/13 07:12:20 Online (Green Mode) - Entered

9/12/13 07:12:27 Online (Green Mode) - Exited

9/12/13 07:12:27 Power Failed

9/12/13 07:12:28 Power Restored

9/12/13 07:12:28 Online (Green Mode) - Entered

9/12/13 07:12:36 Online (Green Mode) - Exited

9/12/13 07:12:36 Power Failed

9/12/13 07:12:38 Power Restored

9/12/13 07:12:38 Online (Green Mode) - Entered

9/12/13 07:12:43 Online (Green Mode) - Exited

9/12/13 07:12:43 Power Failed

9/12/13 07:12:44 Power Restored

9/12/13 07:12:44 Online (Green Mode) - Entered

9/12/13 07:13:28 Online (Green Mode) - Exited

9/12/13 07:13:28 Power Failed

9/12/13 07:13:30 Power Restored

9/12/13 07:13:30 Online (Green Mode) - Entered

9/12/13 07:14:50 Online (Green Mode) - Exited

9/12/13 07:14:50 Power Failed

9/12/13 07:14:51 Power Restored

9/12/13 07:14:51 Online (Green Mode) - Entered

9/12/13 07:14:59 Online (Green Mode) - Exited

9/12/13 07:14:59 Power Failed

9/12/13 07:15:00 Power Restored

9/12/13 07:15:00 Online (Green Mode) - Entered

9/12/13 08:08:15 Online (Green Mode) - Exited

9/12/13 08:08:15 Power Failed

9/12/13 08:08:16 Power Restored

9/12/13 08:08:16 Online (Green Mode) - Entered

9/12/13 08:08:32 Online (Green Mode) - Exited

9/12/13 08:08:32 Power Failed

9/12/13 08:08:33 Power Restored

9/12/13 08:08:33 Online (Green Mode) - Entered

9/12/13 08:08:40 Online (Green Mode) - Exited

9/12/13 08:08:40 Power Failed

9/12/13 08:08:41 Power Restored

9/12/13 08:08:41 Online (Green Mode) - Entered

9/12/13 08:08:44 Online (Green Mode) - Exited

9/12/13 08:08:44 Power Failed

9/12/13 08:08:45 Power Restored

9/12/13 08:08:45 Online (Green Mode) - Entered

9/12/13 08:08:48 Online (Green Mode) - Exited

9/12/13 08:08:48 Power Failed

9/12/13 08:08:49 Power Restored

9/12/13 08:08:49 Online (Green Mode) - Entered

9/12/13 08:08:51 Online (Green Mode) - Exited

9/12/13 08:08:51 Power Failed

9/12/13 08:08:52 Power Restored

9/12/13 08:08:52 Online (Green Mode) - Entered

9/12/13 08:08:53 Online (Green Mode) - Exited

9/12/13 08:08:53 Power Failed

9/12/13 08:08:54 Power Restored

9/12/13 08:08:54 Online (Green Mode) - Entered

9/12/13 08:09:03 Online (Green Mode) - Exited

9/12/13 08:09:03 Power Failed

9/12/13 08:09:04 Power Restored

9/12/13 08:09:04 Online (Green Mode) - Entered

9/12/13 08:09:06 Online (Green Mode) - Exited

9/12/13 08:09:06 Power Failed

9/12/13 08:09:07 Power Restored

9/12/13 08:09:07 Online (Green Mode) - Entered

9/12/13 08:09:12 Online (Green Mode) - Exited

9/12/13 08:09:12 Power Failed

9/12/13 08:09:13 Power Restored

9/12/13 08:09:13 Online (Green Mode) - Entered

9/12/13 08:09:16 Online (Green Mode) - Exited

9/12/13 08:09:16 Power Failed

9/12/13 08:09:17 Power Restored

9/12/13 08:09:17 Online (Green Mode) - Entered

9/12/13 08:09:26 Online (Green Mode) - Exited

9/12/13 08:09:26 Power Failed

9/12/13 08:09:27 Power Restored

9/12/13 08:09:27 Online (Green Mode) - Entered

9/12/13 08:09:47 Online (Green Mode) - Exited

9/12/13 08:09:47 Power Failed

9/12/13 08:09:48 Power Restored

9/12/13 08:09:48 Online (Green Mode) - Entered

9/12/13 08:09:53 Online (Green Mode) - Exited

9/12/13 08:09:53 Power Failed

9/12/13 08:09:54 Power Restored

9/12/13 08:09:54 Online (Green Mode) - Entered

9/12/13 08:10:49 Online (Green Mode) - Exited

9/12/13 08:10:49 Power Failed

9/12/13 08:10:50 Power Restored

9/12/13 08:10:50 Online (Green Mode) - Entered

9/12/13 08:11:06 Online (Green Mode) - Exited

9/12/13 08:11:06 Power Failed

9/12/13 08:11:07 Power Restored

9/12/13 08:11:07 Online (Green Mode) - Entered

9/12/13 08:11:08 Online (Green Mode) - Exited

9/12/13 08:11:08 Power Failed

9/12/13 08:11:09 Power Restored

9/12/13 08:11:09 Online (Green Mode) - Entered

9/12/13 08:12:15 Online (Green Mode) - Exited

9/12/13 08:12:15 Power Failed

9/12/13 08:12:16 Power Restored

9/12/13 08:12:16 Online (Green Mode) - Entered

9/12/13 08:12:27 Online (Green Mode) - Exited

9/12/13 08:12:27 Power Failed

9/12/13 08:12:28 Power Restored

9/12/13 08:12:28 Online (Green Mode) - Entered

9/12/13 08:14:16 Online (Green Mode) - Exited

9/12/13 08:14:16 Power Failed

9/12/13 08:14:17 Power Restored

9/12/13 08:14:17 Online (Green Mode) - Entered

9/12/13 08:17:48 Online (Green Mode) - Exited

9/12/13 08:17:48 Power Failed

9/12/13 08:17:49 Power Restored

9/12/13 08:17:49 Online (Green Mode) - Entered

9/12/13 08:24:34 Online (Green Mode) - Exited

9/12/13 08:24:34 Power Failed

9/12/13 08:24:35 Power Restored

9/12/13 08:24:35 Online (Green Mode) - Entered

9/12/13 08:25:03 Online (Green Mode) - Exited

9/12/13 08:25:03 Power Failed

9/12/13 08:25:04 Power Restored

9/12/13 08:25:04 Online (Green Mode) - Entered

9/12/13 08:25:42 Online (Green Mode) - Exited

9/12/13 08:25:42 Power Failed

9/12/13 08:25:43 Power Restored

9/12/13 08:25:43 Online (Green Mode) - Entered

9/12/13 08:55:23 Online (Green Mode) - Exited

9/12/13 08:55:23 Power Failed

9/12/13 08:55:24 Power Restored

9/12/13 08:55:24 Online (Green Mode) - Entered

9/12/13 08:55:32 Online (Green Mode) - Exited

9/12/13 08:55:32 Power Failed

9/12/13 08:55:33 Power Restored

9/12/13 08:55:33 Online (Green Mode) - Entered

9/12/13 08:56:26 Online (Green Mode) - Exited

9/12/13 08:56:26 Power Failed

9/12/13 08:56:27 Power Restored

9/12/13 08:56:27 Online (Green Mode) - Entered

9/12/13 08:56:37 Online (Green Mode) - Exited

9/12/13 08:56:37 Power Failed

9/12/13 08:56:38 Power Restored

9/12/13 08:56:38 Online (Green Mode) - Entered

9/12/13 08:56:50 Online (Green Mode) - Exited

9/12/13 08:56:50 Power Failed

9/12/13 08:56:51 Power Restored

9/12/13 08:56:51 Online (Green Mode) - Entered

9/12/13 08:57:00 Online (Green Mode) - Exited

9/12/13 08:57:00 Power Failed

9/12/13 08:57:01 Power Restored

9/12/13 08:57:01 Online (Green Mode) - Entered

9/12/13 08:57:07 Online (Green Mode) - Exited

9/12/13 08:57:07 Power Failed

9/12/13 08:57:08 Power Restored

9/12/13 08:57:08 Online (Green Mode) - Entered

9/12/13 08:57:14 Online (Green Mode) - Exited

9/12/13 08:57:14 Power Failed

9/12/13 08:57:15 Power Restored

9/12/13 08:57:15 Online (Green Mode) - Entered

9/12/13 08:57:25 Online (Green Mode) - Exited

9/12/13 08:57:25 Power Failed

9/12/13 08:57:26 Power Restored

9/12/13 08:57:26 Online (Green Mode) - Entered

9/12/13 08:57:27 Online (Green Mode) - Exited

9/12/13 08:57:27 Power Failed

9/12/13 08:57:28 Power Restored

9/12/13 08:57:28 Online (Green Mode) - Entered

9/12/13 08:57:32 Online (Green Mode) - Exited

9/12/13 08:57:32 Power Failed

9/12/13 08:57:33 Power Restored

9/12/13 08:57:33 Online (Green Mode) - Entered

9/12/13 08:57:41 Online (Green Mode) - Exited

9/12/13 08:57:41 Power Failed

9/12/13 08:57:42 Power Restored

9/12/13 08:57:42 Online (Green Mode) - Entered

9/12/13 08:57:52 Online (Green Mode) - Exited

9/12/13 08:57:52 Power Failed

9/12/13 08:57:53 Power Restored

9/12/13 08:57:53 Online (Green Mode) - Entered

9/12/13 08:58:28 Online (Green Mode) - Exited

9/12/13 08:58:28 Power Failed

9/12/13 08:58:29 Power Restored

9/12/13 08:58:29 Online (Green Mode) - Entered

9/12/13 08:58:31 Online (Green Mode) - Exited

9/12/13 08:58:31 Power Failed

9/12/13 08:58:32 Power Restored

9/12/13 08:58:32 Online (Green Mode) - Entered

9/12/13 08:58:39 Online (Green Mode) - Exited

9/12/13 08:58:39 Power Failed

9/12/13 08:58:41 Power Restored

9/12/13 08:58:41 Online (Green Mode) - Entered

9/12/13 08:58:45 Online (Green Mode) - Exited

9/12/13 08:58:45 Power Failed

9/12/13 08:58:46 Power Restored

9/12/13 08:58:46 Online (Green Mode) - Entered

9/12/13 08:58:57 Online (Green Mode) - Exited

9/12/13 08:58:57 Power Failed

9/12/13 08:58:58 Power Restored

9/12/13 08:58:58 Online (Green Mode) - Entered

9/12/13 09:11:47 Online (Green Mode) - Exited

9/12/13 09:11:47 Power Failed

9/12/13 09:11:49 Power Restored

9/12/13 09:11:49 Online (Green Mode) - Entered

9/12/13 09:11:51 Online (Green Mode) - Exited

9/12/13 09:11:51 Power Failed

9/12/13 09:11:52 Power Restored

9/12/13 09:11:52 Online (Green Mode) - Entered

9/12/13 09:11:54 Online (Green Mode) - Exited

9/12/13 09:11:54 Power Failed

9/12/13 09:11:55 Power Restored

9/12/13 09:11:55 Online (Green Mode) - Entered

9/12/13 09:11:57 Online (Green Mode) - Exited

9/12/13 09:11:57 Power Failed

9/12/13 09:11:58 Power Restored

9/12/13 09:11:58 Online (Green Mode) - Entered

9/12/13 09:12:37 Online (Green Mode) - Exited

9/12/13 09:12:37 Power Failed

9/12/13 09:12:38 Power Restored

9/12/13 09:12:38 Online (Green Mode) - Entered

9/12/13 09:12:51 Online (Green Mode) - Exited

9/12/13 09:12:51 Power Failed

9/12/13 09:12:52 Power Restored

9/12/13 09:12:52 Online (Green Mode) - Entered

9/12/13 09:13:04 Online (Green Mode) - Exited

9/12/13 09:13:04 Power Failed

9/12/13 09:13:05 Power Restored

9/12/13 09:13:05 Online (Green Mode) - Entered

9/12/13 09:13:51 Online (Green Mode) - Exited

9/12/13 09:13:51 Power Failed

9/12/13 09:13:52 Power Restored

9/12/13 09:13:52 Online (Green Mode) - Entered

9/12/13 09:15:11 Online (Green Mode) - Exited

9/12/13 09:15:11 Power Failed

9/12/13 09:15:12 Power Restored

9/12/13 09:15:12 Online (Green Mode) - Entered

9/12/13 09:15:22 Online (Green Mode) - Exited

9/12/13 09:15:22 Power Failed

9/12/13 09:15:23 Power Restored

9/12/13 09:15:23 Online (Green Mode) - Entered

9/12/13 09:15:28 Online (Green Mode) - Exited

9/12/13 09:15:28 Power Failed

9/12/13 09:15:29 Power Restored

9/12/13 09:15:29 Online (Green Mode) - Entered

9/12/13 09:17:28 Online (Green Mode) - Exited

9/12/13 09:17:28 Power Failed

9/12/13 09:17:29 Power Restored

9/12/13 09:17:29 Online (Green Mode) - Entered

9/12/13 09:17:36 Online (Green Mode) - Exited

9/12/13 09:17:36 Power Failed

9/12/13 09:17:38 Power Restored

9/12/13 09:17:38 Online (Green Mode) - Entered

9/12/13 09:17:42 Online (Green Mode) - Exited

9/12/13 09:17:42 Power Failed

9/12/13 09:17:43 Power Restored

9/12/13 09:17:43 Online (Green Mode) - Entered

9/12/13 09:17:52 Online (Green Mode) - Exited

9/12/13 09:17:52 Power Failed

9/12/13 09:17:53 Power Restored

9/12/13 09:17:53 Online (Green Mode) - Entered

9/12/13 09:18:04 Online (Green Mode) - Exited

9/12/13 09:18:04 Power Failed

9/12/13 09:18:05 Power Restored

9/12/13 09:18:05 Online (Green Mode) - Entered

9/12/13 09:18:36 Online (Green Mode) - Exited

9/12/13 09:18:36 Power Failed

9/12/13 09:18:37 Power Restored

9/12/13 09:18:37 Online (Green Mode) - Entered

9/12/13 09:41:30 Online (Green Mode) - Exited

9/12/13 09:41:30 Power Failed

9/12/13 09:41:31 Power Restored

9/12/13 09:41:31 Online (Green Mode) - Entered

9/12/13 09:41:49 Online (Green Mode) - Exited

9/12/13 09:41:49 Power Failed

9/12/13 09:41:50 Power Restored

9/12/13 09:41:50 Online (Green Mode) - Entered

9/12/13 09:41:52 Online (Green Mode) - Exited

9/12/13 09:41:52 Power Failed

9/12/13 09:41:53 Power Restored

9/12/13 09:41:53 Online (Green Mode) - Entered

9/12/13 09:41:55 Online (Green Mode) - Exited

9/12/13 09:41:55 Power Failed

9/12/13 09:41:57 Power Restored

9/12/13 09:41:57 Online (Green Mode) - Entered

9/12/13 09:42:02 Online (Green Mode) - Exited

9/12/13 09:42:02 Power Failed

9/12/13 09:42:03 Power Restored

9/12/13 09:42:03 Online (Green Mode) - Entered

9/12/13 09:42:07 Online (Green Mode) - Exited

9/12/13 09:42:07 Power Failed

9/12/13 09:42:08 Power Restored

9/12/13 09:42:08 Online (Green Mode) - Entered

9/12/13 09:42:09 Online (Green Mode) - Exited

9/12/13 09:42:09 Power Failed

9/12/13 09:42:10 Power Restored

9/12/13 09:42:10 Online (Green Mode) - Entered

9/12/13 09:42:12 Online (Green Mode) - Exited

9/12/13 09:42:12 Power Failed

9/12/13 09:42:13 Power Restored

9/12/13 09:42:13 Online (Green Mode) - Entered

9/12/13 09:42:14 Online (Green Mode) - Exited

9/12/13 09:42:14 Power Failed

9/12/13 09:42:15 Power Restored

9/12/13 09:42:15 Online (Green Mode) - Entered

9/12/13 09:42:18 Online (Green Mode) - Exited

9/12/13 09:42:18 Power Failed

9/12/13 09:42:19 Power Restored

9/12/13 09:42:19 Online (Green Mode) - Entered

9/12/13 09:42:21 Online (Green Mode) - Exited

9/12/13 09:42:21 Power Failed

9/12/13 09:42:22 Power Restored

9/12/13 09:42:22 Online (Green Mode) - Entered

9/12/13 09:42:25 Online (Green Mode) - Exited

9/12/13 09:42:25 Power Failed

9/12/13 09:42:28 Power Restored

9/12/13 09:42:28 Online (Green Mode) - Entered

9/12/13 09:42:32 Online (Green Mode) - Exited

9/12/13 09:42:32 Power Failed

9/12/13 09:42:33 Power Restored

9/12/13 09:42:33 Online (Green Mode) - Entered

9/12/13 09:42:34 Online (Green Mode) - Exited

9/12/13 09:42:34 Power Failed

9/12/13 09:42:35 Power Restored

9/12/13 09:42:35 Online (Green Mode) - Entered

9/12/13 09:42:37 Online (Green Mode) - Exited

9/12/13 09:42:37 Power Failed

9/12/13 09:42:38 Power Restored

9/12/13 09:42:38 Online (Green Mode) - Entered

9/12/13 09:42:44 Online (Green Mode) - Exited

9/12/13 09:42:44 Power Failed

9/12/13 09:42:45 Power Restored

9/12/13 09:42:45 Online (Green Mode) - Entered

9/12/13 09:42:55 Online (Green Mode) - Exited

9/12/13 09:42:55 Power Failed

9/12/13 09:42:57 Power Restored

9/12/13 09:42:57 Online (Green Mode) - Entered

9/12/13 09:43:00 Online (Green Mode) - Exited

9/12/13 09:43:00 Power Failed

9/12/13 09:43:01 Power Restored

9/12/13 09:43:01 Online (Green Mode) - Entered

9/12/13 09:43:02 Online (Green Mode) - Exited

9/12/13 09:43:02 Power Failed

9/12/13 09:43:03 Power Restored

9/12/13 09:43:03 Online (Green Mode) - Entered

9/12/13 09:43:15 Online (Green Mode) - Exited

9/12/13 09:43:15 Power Failed

9/12/13 09:43:16 Power Restored

9/12/13 09:43:16 Online (Green Mode) - Entered

9/12/13 09:43:23 Online (Green Mode) - Exited

9/12/13 09:43:23 Power Failed

9/12/13 09:43:24 Power Restored

9/12/13 09:43:24 Online (Green Mode) - Entered

9/12/13 09:43:26 Online (Green Mode) - Exited

9/12/13 09:43:26 Power Failed

9/12/13 09:43:27 Power Restored

9/12/13 09:43:27 Online (Green Mode) - Entered

9/12/13 09:43:34 Online (Green Mode) - Exited

9/12/13 09:43:34 Power Failed

9/12/13 09:43:35 Power Restored

9/12/13 09:43:35 Online (Green Mode) - Entered

9/12/13 09:43:46 Online (Green Mode) - Exited

9/12/13 09:43:46 Power Failed

9/12/13 09:43:47 Power Restored

9/12/13 09:43:47 Online (Green Mode) - Entered

9/12/13 09:43:52 Online (Green Mode) - Exited

9/12/13 09:43:52 Power Failed

9/12/13 09:43:53 Power Restored

9/12/13 09:43:53 Online (Green Mode) - Entered

9/12/13 09:44:07 Online (Green Mode) - Exited

9/12/13 09:44:07 Power Failed

9/12/13 09:44:08 Power Restored

9/12/13 09:44:08 Online (Green Mode) - Entered

9/12/13 09:44:11 Online (Green Mode) - Exited

9/12/13 09:44:11 Power Failed

9/12/13 09:44:12 Power Restored

9/12/13 09:44:12 Online (Green Mode) - Entered

9/12/13 09:44:13 Online (Green Mode) - Exited

9/12/13 09:44:13 Power Failed

9/12/13 09:44:15 Power Restored

9/12/13 09:44:15 Online (Green Mode) - Entered

9/12/13 09:44:18 Online (Green Mode) - Exited

9/12/13 09:44:18 Power Failed

9/12/13 09:44:19 Power Restored

9/12/13 09:44:19 Online (Green Mode) - Entered

9/12/13 09:44:29 Online (Green Mode) - Exited

9/12/13 09:44:29 Power Failed

9/12/13 09:44:30 Power Restored

9/12/13 09:44:30 Online (Green Mode) - Entered

9/12/13 09:44:31 Online (Green Mode) - Exited

9/12/13 09:44:31 Power Failed

9/12/13 09:44:32 Power Restored

9/12/13 09:44:32 Online (Green Mode) - Entered

9/12/13 09:44:36 Online (Green Mode) - Exited

9/12/13 09:44:36 Power Failed

9/12/13 09:44:37 Power Restored

9/12/13 09:44:37 Online (Green Mode) - Entered

9/12/13 09:44:38 Online (Green Mode) - Exited

9/12/13 09:44:38 Power Failed

9/12/13 09:44:40 Power Restored

9/12/13 09:44:40 Online (Green Mode) - Entered

9/12/13 09:44:44 Online (Green Mode) - Exited

9/12/13 09:44:44 Power Failed

9/12/13 09:44:45 Power Restored

9/12/13 09:44:45 Online (Green Mode) - Entered

9/12/13 09:44:56 Online (Green Mode) - Exited

9/12/13 09:44:56 Power Failed

9/12/13 09:44:57 Power Restored

9/12/13 09:44:57 Online (Green Mode) - Entered

9/12/13 09:45:04 Online (Green Mode) - Exited

9/12/13 09:45:04 Power Failed

9/12/13 09:45:05 Power Restored

9/12/13 09:45:05 Online (Green Mode) - Entered

9/12/13 09:45:09 Online (Green Mode) - Exited

9/12/13 09:45:09 Power Failed

9/12/13 09:45:12 Power Restored

9/12/13 09:45:12 Online (Green Mode) - Entered

9/12/13 09:45:31 Online (Green Mode) - Exited

9/12/13 09:45:31 Power Failed

9/12/13 09:45:32 Power Restored

9/12/13 09:45:32 Online (Green Mode) - Entered

9/12/13 09:45:49 Online (Green Mode) - Exited

9/12/13 09:45:49 Power Failed

9/12/13 09:45:50 Power Restored

9/12/13 09:45:50 Online (Green Mode) - Entered

9/12/13 09:46:02 Online (Green Mode) - Exited

9/12/13 09:46:02 Power Failed

9/12/13 09:46:03 Power Restored

9/12/13 09:46:03 Online (Green Mode) - Entered

9/12/13 09:46:09 Online (Green Mode) - Exited

9/12/13 09:46:09 Power Failed

9/12/13 09:46:10 Power Restored

9/12/13 09:46:10 Online (Green Mode) - Entered

9/12/13 09:46:15 Online (Green Mode) - Exited

9/12/13 09:46:15 Power Failed

9/12/13 09:46:16 Power Restored

9/12/13 09:46:16 Online (Green Mode) - Entered

9/12/13 09:46:27 Online (Green Mode) - Exited

9/12/13 09:46:27 Power Failed

9/12/13 09:46:28 Power Restored

9/12/13 09:46:28 Online (Green Mode) - Entered

9/12/13 09:46:43 Online (Green Mode) - Exited

9/12/13 09:46:43 Power Failed

9/12/13 09:46:44 Power Restored

9/12/13 09:46:44 Online (Green Mode) - Entered

9/12/13 09:47:07 Online (Green Mode) - Exited

9/12/13 09:47:07 Power Failed

9/12/13 09:47:08 Power Restored

9/12/13 09:47:08 Online (Green Mode) - Entered

9/12/13 09:47:11 Online (Green Mode) - Exited

9/12/13 09:47:11 Power Failed

9/12/13 09:47:12 Power Restored

9/12/13 09:47:12 Online (Green Mode) - Entered

9/12/13 09:48:02 Online (Green Mode) - Exited

9/12/13 09:48:02 Power Failed

9/12/13 09:48:03 Power Restored

9/12/13 09:48:03 Online (Green Mode) - Entered

9/12/13 09:49:05 Online (Green Mode) - Exited

9/12/13 09:49:05 Power Failed

9/12/13 09:49:06 Power Restored

9/12/13 09:49:06 Online (Green Mode) - Entered

9/12/13 09:56:57 Online (Green Mode) - Exited

9/12/13 09:56:57 Power Failed

9/12/13 09:56:58 Power Restored

9/12/13 09:56:58 Online (Green Mode) - Entered

9/12/13 10:26:03 Online (Green Mode) - Exited

9/12/13 10:26:03 Power Failed

9/12/13 10:26:04 Power Restored

9/12/13 10:26:04 Online (Green Mode) - Entered

9/12/13 10:26:05 Online (Green Mode) - Exited

9/12/13 10:26:05 Power Failed

9/12/13 10:26:06 Power Restored

9/12/13 10:26:06 Online (Green Mode) - Entered

9/12/13 10:27:00 Online (Green Mode) - Exited

9/12/13 10:27:00 Power Failed

9/12/13 10:27:01 Power Restored

9/12/13 10:27:01 Online (Green Mode) - Entered

9/12/13 10:27:13 Online (Green Mode) - Exited

9/12/13 10:27:13 Power Failed

9/12/13 10:27:14 Power Restored

9/12/13 10:27:14 Online (Green Mode) - Entered

9/12/13 10:27:57 Online (Green Mode) - Exited

9/12/13 10:27:57 Power Failed

9/12/13 10:27:58 Power Restored

9/12/13 10:27:58 Online (Green Mode) - Entered

9/12/13 10:28:12 Online (Green Mode) - Exited

9/12/13 10:28:12 Power Failed

9/12/13 10:28:13 Power Restored

9/12/13 10:28:13 Online (Green Mode) - Entered

9/12/13 10:28:22 Online (Green Mode) - Exited

9/12/13 10:28:22 Power Failed

9/12/13 10:28:23 Power Restored

9/12/13 10:28:23 Online (Green Mode) - Entered

9/12/13 10:28:43 Online (Green Mode) - Exited

9/12/13 10:28:43 Power Failed

9/12/13 10:28:44 Power Restored

9/12/13 10:28:44 Online (Green Mode) - Entered

9/12/13 10:28:52 Online (Green Mode) - Exited

9/12/13 10:28:52 Power Failed

9/12/13 10:28:53 Power Restored

9/12/13 10:28:53 Online (Green Mode) - Entered

9/12/13 10:29:21 Online (Green Mode) - Exited

9/12/13 10:29:21 Power Failed

9/12/13 10:29:22 Power Restored

9/12/13 10:29:22 Online (Green Mode) - Entered

9/12/13 10:29:24 Online (Green Mode) - Exited

9/12/13 10:29:24 Power Failed

9/12/13 10:29:25 Power Restored

9/12/13 10:29:25 Online (Green Mode) - Entered

9/12/13 10:29:31 Online (Green Mode) - Exited

9/12/13 10:29:31 Power Failed

9/12/13 10:29:32 Power Restored

9/12/13 10:29:32 Online (Green Mode) - Entered

9/12/13 10:29:51 Online (Green Mode) - Exited

9/12/13 10:29:51 Power Failed

9/12/13 10:29:52 Power Restored

9/12/13 10:29:52 Online (Green Mode) - Entered

9/12/13 10:30:09 Online (Green Mode) - Exited

9/12/13 10:30:09 Power Failed

9/12/13 10:30:10 Power Restored

9/12/13 10:30:10 Online (Green Mode) - Entered

9/12/13 10:30:55 Online (Green Mode) - Exited

9/12/13 10:30:55 Power Failed

9/12/13 10:30:56 Power Restored

9/12/13 10:30:56 Online (Green Mode) - Entered

9/12/13 10:31:03 Online (Green Mode) - Exited

9/12/13 10:31:03 Power Failed

9/12/13 10:31:04 Power Restored

9/12/13 10:31:04 Online (Green Mode) - Entered

9/12/13 10:32:46 Online (Green Mode) - Exited

9/12/13 10:32:46 Power Failed

9/12/13 10:32:47 Power Restored

9/12/13 10:32:47 Online (Green Mode) - Entered

9/12/13 10:33:04 Online (Green Mode) - Exited

9/12/13 10:33:04 Power Failed

9/12/13 10:33:05 Power Restored

9/12/13 10:33:05 Online (Green Mode) - Entered

9/12/13 10:33:08 Online (Green Mode) - Exited

9/12/13 10:33:08 Power Failed

9/12/13 10:33:09 Power Restored

9/12/13 10:33:09 Online (Green Mode) - Entered

9/12/13 10:42:41 Online (Green Mode) - Exited

9/12/13 10:42:41 Power Failed

9/12/13 10:42:42 Power Restored

9/12/13 10:42:42 Online (Green Mode) - Entered

9/12/13 10:47:40 Online (Green Mode) - Exited

9/12/13 10:47:40 Power Failed

9/12/13 10:47:42 Power Restored

9/12/13 10:47:42 Online (Green Mode) - Entered

9/12/13 11:30:16 Online (Green Mode) - Exited

9/12/13 11:30:16 Power Failed

9/12/13 11:30:17 Power Restored

9/12/13 11:30:17 Online (Green Mode) - Entered

9/12/13 12:03:14 Online (Green Mode) - Exited

9/12/13 12:03:14 Power Failed

9/12/13 12:03:15 Power Restored

9/12/13 12:03:15 Online (Green Mode) - Entered

9/12/13 12:22:41 Online (Green Mode) - Exited

9/12/13 12:22:41 Power Failed

9/12/13 12:22:42 Power Restored

9/12/13 12:22:42 Online (Green Mode) - Entered

9/12/13 19:35:03 Online (Green Mode) - Exited

9/12/13 19:35:03 Power Failed

9/12/13 19:35:04 Power Restored

9/12/13 19:35:04 Online (Green Mode) - Entered

9/12/13 19:57:33 Online (Green Mode) - Exited

9/12/13 19:57:33 Power Failed

9/12/13 19:57:34 Power Restored

9/12/13 19:57:34 Online (Green Mode) - Entered

9/12/13 23:14:59 Online (Green Mode) - Exited

9/12/13 23:14:59 Power Failed

9/12/13 23:15:00 Power Restored

9/12/13 23:15:00 Online (Green Mode) - Entered

9/13/13 00:00:59 Online (Green Mode) - Exited

9/13/13 00:00:59 Power Failed

9/13/13 00:01:00 Power Restored

9/13/13 00:01:00 Online (Green Mode) - Entered

9/13/13 12:13:08 Online (Green Mode) - Exited

9/13/13 12:13:08 Power Failed

9/13/13 12:13:18 Power Restored

9/13/13 12:13:18 Online (Green Mode) - Entered

9/13/13 12:13:19 Online (Green Mode) - Exited

9/13/13 12:13:19 Power Failed

9/13/13 12:13:24 Power Restored

9/13/13 12:13:24 Online (Green Mode) - Entered

9/13/13 12:13:25 Online (Green Mode) - Exited

9/13/13 12:13:25 Power Failed

9/13/13 12:13:27 Power Restored

9/13/13 12:13:27 Online (Green Mode) - Entered

9/13/13 12:13:28 Online (Green Mode) - Exited

9/13/13 12:13:28 Power Failed

9/13/13 12:13:29 Power Restored

9/13/13 12:13:29 Online (Green Mode) - Entered

9/13/13 12:13:30 Online (Green Mode) - Exited

9/13/13 12:13:30 Power Failed

9/13/13 12:13:32 Power Restored

9/13/13 12:13:32 Online (Green Mode) - Entered

9/13/13 12:13:33 Online (Green Mode) - Exited

9/13/13 12:13:33 Power Failed

9/13/13 12:13:38 Power Restored

9/13/13 12:13:38 Online (Green Mode) - Entered

9/13/13 12:13:39 Online (Green Mode) - Exited

9/13/13 12:13:39 Power Failed

9/13/13 12:13:41 Power Restored

9/13/13 12:13:41 Online (Green Mode) - Entered

9/13/13 12:13:42 Online (Green Mode) - Exited

9/13/13 12:13:42 Power Failed

9/13/13 12:13:47 Power Restored

9/13/13 12:13:47 Online (Green Mode) - Entered

9/13/13 12:13:49 Online (Green Mode) - Exited

9/13/13 12:13:49 Power Failed

9/13/13 12:13:50 Power Restored

9/13/13 12:13:50 Online (Green Mode) - Entered

9/13/13 12:13:51 Online (Green Mode) - Exited

9/13/13 12:13:51 Power Failed

9/13/13 12:13:53 Power Restored

9/13/13 12:13:53 Online (Green Mode) - Entered

9/13/13 12:13:55 Online (Green Mode) - Exited

9/13/13 12:13:55 Power Failed

9/13/13 12:13:56 Power Restored

9/13/13 12:13:56 Online (Green Mode) - Entered

9/13/13 12:13:57 Online (Green Mode) - Exited

9/13/13 12:13:57 Power Failed

9/13/13 12:13:59 Power Restored

9/13/13 12:13:59 Online (Green Mode) - Entered

9/13/13 12:14:00 Online (Green Mode) - Exited

9/13/13 12:14:00 Power Failed

9/13/13 12:14:04 Power Restored

9/13/13 12:14:04 Online (Green Mode) - Entered

9/13/13 12:14:05 Online (Green Mode) - Exited

9/13/13 12:14:05 Power Failed

9/13/13 12:14:09 Power Restored

9/13/13 12:14:09 Online (Green Mode) - Entered

9/13/13 12:14:11 Online (Green Mode) - Exited

9/13/13 12:14:11 Power Failed

9/13/13 12:14:12 Power Restored

9/13/13 12:14:12 Online (Green Mode) - Entered

9/13/13 12:14:14 Online (Green Mode) - Exited

9/13/13 12:14:14 Power Failed

9/13/13 12:14:15 Power Restored

9/13/13 12:14:15 Online (Green Mode) - Entered

9/13/13 12:14:16 Online (Green Mode) - Exited

9/13/13 12:14:16 Power Failed

9/13/13 12:14:18 Power Restored

9/13/13 12:14:18 Online (Green Mode) - Entered

9/13/13 12:14:19 Online (Green Mode) - Exited

9/13/13 12:14:19 Power Failed

9/13/13 12:14:21 Power Restored

9/13/13 12:14:21 Online (Green Mode) - Entered

9/13/13 12:14:23 Online (Green Mode) - Exited

9/13/13 12:14:23 Power Failed

9/13/13 12:14:24 Power Restored

9/13/13 12:14:24 Online (Green Mode) - Entered

9/13/13 12:14:25 Online (Green Mode) - Exited

9/13/13 12:14:25 Power Failed

9/13/13 12:14:31 Power Restored

9/13/13 12:14:31 Online (Green Mode) - Entered

9/13/13 12:14:32 Online (Green Mode) - Exited

9/13/13 12:14:32 Power Failed

9/13/13 12:14:33 Power Restored

9/13/13 12:14:33 Online (Green Mode) - Entered

9/13/13 12:14:34 Online (Green Mode) - Exited

9/13/13 12:14:34 Power Failed

9/13/13 12:14:36 Power Restored

9/13/13 12:14:36 Online (Green Mode) - Entered

9/13/13 12:14:37 Online (Green Mode) - Exited

9/13/13 12:14:37 Power Failed

9/13/13 12:14:42 Power Restored

9/13/13 12:14:42 Online (Green Mode) - Entered

9/13/13 12:14:43 Online (Green Mode) - Exited

9/13/13 12:14:43 Power Failed

9/13/13 12:14:45 Power Restored

9/13/13 12:14:45 Online (Green Mode) - Entered

9/13/13 12:14:46 Online (Green Mode) - Exited

9/13/13 12:14:46 Power Failed

9/13/13 12:14:54 Power Restored

9/13/13 12:14:54 Online (Green Mode) - Entered

9/13/13 12:14:55 Online (Green Mode) - Exited

9/13/13 12:14:55 Power Failed

9/13/13 12:14:56 Power Restored

9/13/13 12:14:56 Online (Green Mode) - Entered

9/13/13 12:14:57 Online (Green Mode) - Exited

9/13/13 12:14:57 Power Failed

9/13/13 12:15:03 Power Restored

9/13/13 12:15:03 Online (Green Mode) - Entered

9/13/13 12:15:04 Online (Green Mode) - Exited

9/13/13 12:15:04 Power Failed

9/13/13 12:15:05 Power Restored

9/13/13 12:15:05 Online (Green Mode) - Entered

9/13/13 12:15:06 Online (Green Mode) - Exited

9/13/13 12:15:06 Power Failed

9/13/13 12:15:08 Power Restored

9/13/13 12:15:08 Online (Green Mode) - Entered

9/13/13 12:15:09 Online (Green Mode) - Exited

9/13/13 12:15:09 Power Failed

9/13/13 12:15:14 Power Restored

9/13/13 12:15:14 Online (Green Mode) - Entered

9/13/13 12:15:15 Online (Green Mode) - Exited

9/13/13 12:15:15 Power Failed

9/13/13 12:15:17 Power Restored

9/13/13 12:15:17 Online (Green Mode) - Entered

9/13/13 12:15:18 Online (Green Mode) - Exited

9/13/13 12:15:18 Power Failed

9/13/13 12:15:23 Power Restored

9/13/13 12:15:23 Online (Green Mode) - Entered

9/13/13 12:15:24 Online (Green Mode) - Exited

9/13/13 12:15:24 Power Failed

9/13/13 12:15:26 Power Restored

9/13/13 12:15:26 Online (Green Mode) - Entered

9/13/13 12:15:27 Online (Green Mode) - Exited

9/13/13 12:15:27 Power Failed

9/13/13 12:15:28 Power Restored

9/13/13 12:15:28 Online (Green Mode) - Entered

9/13/13 12:15:29 Online (Green Mode) - Exited

9/13/13 12:15:29 Power Failed

9/13/13 12:15:32 Power Restored

9/13/13 12:15:32 Online (Green Mode) - Entered

9/13/13 12:15:33 Online (Green Mode) - Exited

9/13/13 12:15:33 Power Failed

9/13/13 12:15:35 Power Restored

9/13/13 12:15:35 Online (Green Mode) - Entered

9/13/13 12:15:36 Online (Green Mode) - Exited

9/13/13 12:15:36 Power Failed

9/13/13 12:15:37 Power Restored

9/13/13 12:15:37 Online (Green Mode) - Entered

9/13/13 12:15:38 Online (Green Mode) - Exited

9/13/13 12:15:38 Power Failed

9/13/13 12:15:40 Power Restored

9/13/13 12:15:40 Online (Green Mode) - Entered

9/13/13 12:15:43 Online (Green Mode) - Exited

9/13/13 12:15:43 Power Failed

9/13/13 12:15:46 Power Restored

9/13/13 12:15:46 Online (Green Mode) - Entered

9/13/13 12:15:47 Online (Green Mode) - Exited

9/13/13 12:15:47 Power Failed

9/13/13 12:15:49 Power Restored

9/13/13 12:15:49 Online (Green Mode) - Entered

9/13/13 12:15:50 Online (Green Mode) - Exited

9/13/13 12:15:50 Power Failed

9/13/13 12:15:53 Power Restored

9/13/13 12:15:53 Online (Green Mode) - Entered

9/13/13 12:15:54 Online (Green Mode) - Exited

9/13/13 12:15:54 Power Failed

9/13/13 12:15:55 Power Restored

9/13/13 12:15:55 Online (Green Mode) - Entered

9/13/13 12:15:56 Online (Green Mode) - Exited

9/13/13 12:15:56 Power Failed

9/13/13 12:15:58 Power Restored

9/13/13 12:15:58 Online (Green Mode) - Entered

9/13/13 12:15:59 Online (Green Mode) - Exited

9/13/13 12:15:59 Power Failed

9/13/13 12:16:02 Power Restored

9/13/13 12:16:02 Online (Green Mode) - Entered

9/13/13 12:16:03 Online (Green Mode) - Exited

9/13/13 12:16:03 Power Failed

9/13/13 12:16:04 Power Restored

9/13/13 12:16:04 Online (Green Mode) - Entered

9/13/13 12:16:05 Online (Green Mode) - Exited

9/13/13 12:16:05 Power Failed

9/13/13 12:16:07 Power Restored

9/13/13 12:16:07 Online (Green Mode) - Entered

9/13/13 12:16:08 Online (Green Mode) - Exited

9/13/13 12:16:08 Power Failed

9/13/13 12:16:10 Power Restored

9/13/13 12:16:10 Online (Green Mode) - Entered

9/13/13 12:16:11 Online (Green Mode) - Exited

9/13/13 12:16:11 Power Failed

9/13/13 12:16:16 Power Restored

9/13/13 12:16:16 Online (Green Mode) - Entered

9/13/13 12:16:17 Online (Green Mode) - Exited

9/13/13 12:16:17 Power Failed

9/13/13 12:16:19 Power Restored

9/13/13 12:16:19 Online (Green Mode) - Entered

9/13/13 12:16:20 Online (Green Mode) - Exited

9/13/13 12:16:20 Power Failed

9/13/13 12:16:21 Power Restored

9/13/13 12:16:21 Online (Green Mode) - Entered

9/13/13 12:16:22 Online (Green Mode) - Exited

9/13/13 12:16:22 Power Failed

9/13/13 12:16:24 Power Restored

9/13/13 12:16:24 Online (Green Mode) - Entered

9/13/13 12:16:25 Online (Green Mode) - Exited

9/13/13 12:16:25 Power Failed

9/13/13 12:16:33 Power Restored

9/13/13 12:16:33 Online (Green Mode) - Entered

9/13/13 12:16:34 Online (Green Mode) - Exited

9/13/13 12:16:34 Power Failed

9/13/13 12:16:36 Power Restored

9/13/13 12:16:36 Online (Green Mode) - Entered

9/13/13 12:16:37 Online (Green Mode) - Exited

9/13/13 12:16:37 Power Failed

9/13/13 12:16:39 Power Restored

9/13/13 12:16:39 Online (Green Mode) - Entered

9/13/13 12:16:40 Online (Green Mode) - Exited

9/13/13 12:16:40 Power Failed

9/13/13 12:16:43 Power Restored

9/13/13 12:16:43 Online (Green Mode) - Entered

9/13/13 12:16:44 Online (Green Mode) - Exited

9/13/13 12:16:44 Power Failed

9/13/13 12:16:45 Power Restored

9/13/13 12:16:45 Online (Green Mode) - Entered

9/13/13 12:16:46 Online (Green Mode) - Exited

9/13/13 12:16:46 Power Failed

9/13/13 12:16:48 Power Restored

9/13/13 12:16:48 Online (Green Mode) - Entered

9/13/13 12:16:49 Online (Green Mode) - Exited

9/13/13 12:16:49 Power Failed

9/13/13 12:16:51 Power Restored

9/13/13 12:16:51 Online (Green Mode) - Entered

9/13/13 12:16:52 Online (Green Mode) - Exited

9/13/13 12:16:52 Power Failed

9/13/13 12:16:54 Power Restored

9/13/13 12:16:54 Online (Green Mode) - Entered

9/13/13 12:16:55 Online (Green Mode) - Exited

9/13/13 12:16:55 Power Failed

9/13/13 12:16:57 Power Restored

9/13/13 12:16:57 Online (Green Mode) - Entered

9/13/13 12:16:58 Online (Green Mode) - Exited

9/13/13 12:16:58 Power Failed

9/13/13 12:17:06 Power Restored

9/13/13 12:17:06 Online (Green Mode) - Entered

9/13/13 12:17:07 Online (Green Mode) - Exited

9/13/13 12:17:07 Power Failed

9/13/13 12:17:08 Power Restored

9/13/13 12:17:08 Online (Green Mode) - Entered

9/13/13 12:17:09 Online (Green Mode) - Exited

9/13/13 12:17:09 Power Failed

9/13/13 12:17:15 Power Restored

9/13/13 12:17:15 Online (Green Mode) - Entered

9/13/13 12:17:16 Online (Green Mode) - Exited

9/13/13 12:17:16 Power Failed

9/13/13 12:17:17 Power Restored

9/13/13 12:17:17 Online (Green Mode) - Entered

9/13/13 12:17:18 Online (Green Mode) - Exited

9/13/13 12:17:18 Power Failed

9/13/13 12:17:20 Power Restored

9/13/13 12:17:20 Online (Green Mode) - Entered

9/13/13 12:17:21 Online (Green Mode) - Exited

9/13/13 12:17:21 Power Failed

9/13/13 12:17:26 Power Restored

9/13/13 12:17:26 Online (Green Mode) - Entered

9/13/13 12:17:27 Online (Green Mode) - Exited

9/13/13 12:17:27 Power Failed

9/13/13 12:17:29 Power Restored

9/13/13 12:17:29 Online (Green Mode) - Entered

9/13/13 12:17:30 Online (Green Mode) - Exited

9/13/13 12:17:30 Power Failed

9/13/13 12:17:33 Monitoring Stopped

9/13/13 13:33:05 Monitoring Started

9/13/13 13:33:36 Communication Not Established

9/13/13 13:34:27 Communication Established

9/13/13 13:34:28 Online (Green Mode) - Entered

BillP
Administrator Administrator
Administrator
0 Likes
0
197

Re: SMX1500RM2U Strange Behavior

This reply was originally posted by Angela on APC forums on 9/16/2013


If you use the advanced editor (an option on the top right of the reply box), you'll get attachment options.

I do see a lot of input voltage fluctuations..

gendoikari_apc
Crewman
Crewman
0 Likes
0
197

Re: SMX1500RM2U Strange Behavior

This was originally posted on APC forums on 9/20/2013


Ahh, I see the advanced editor option now, sorry about that!

Anyhow, I set the sensitivity to low, and not a peep out of the SMX1500RM2U. I'm a bit worried that it may be letting more "noise" through, thou I wouldn't know how to tell. This also is a relief as I was planning on buying a second SMX1500RM2U, and now know what settings to use. Thank you for your time. =3