Posted: 2021-06-29 07:14 AM . Last Modified: 2 weeks ago
Anyone have comments on connecting a UXBP48 to a SMX1000? SMX has a label stating it uses a 48V DC external battery pack, which is what I understand the UXBP48 is.
Any thoughts on using a UXBP48 with 2 year old batteries connected to a three month old SMX1000?
Thanks, I appreciate the groups knowledge and wisdom.
Jeff
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:14 AM . Last Modified: 2 weeks ago
Hi John,
The UXBP48 is not a compatible external battery pack for the SMX1000. The UPS will not be able to detect the battery pack.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:14 AM . Last Modified: 2 weeks ago
Anyone have comments on connecting a UXBP48 to a SMX1000? SMX has a label stating it uses a 48V DC external battery pack, which is what I understand the UXBP48 is.
Any thoughts on using a UXBP48 with 2 year old batteries connected to a three month old SMX1000?
Thanks, I appreciate the groups knowledge and wisdom.
Jeff
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:14 AM . Last Modified: 2 weeks ago
Hi John,
The UXBP48 is not a compatible external battery pack for the SMX1000. The UPS will not be able to detect the battery pack.