SMT1500I battery problem

This question was originally posted by Rasha on APC forums on 9/30/2014


after replace battery with new one UPS not give right run time,please advise if probelm in main board or what?

thanks.

Rasha arafat


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
69

Re: SMT1500I battery problem

This reply was originally posted by Angela on APC forums on 9/30/2014


SMT1500 requires you to adjust the battery replacement date via the front display/LCD to update properly. Did you see a pop up to confirm that you replaced it? If so, does the battery replacement date show today and the predicted battery replacement date show a few years in the future?

You can also try a runtime calibration on this if everything seems updated with the replacement battery date.

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
70

Re: SMT1500I battery problem

This reply was originally posted by Angela on APC forums on 9/30/2014


SMT1500 requires you to adjust the battery replacement date via the front display/LCD to update properly. Did you see a pop up to confirm that you replaced it? If so, does the battery replacement date show today and the predicted battery replacement date show a few years in the future?

You can also try a runtime calibration on this if everything seems updated with the replacement battery date.