APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:45 AM . Last Modified: 2024-03-13 01:26 AM
Rackmountable SC450 that I have at a satellite site is beeping once every 30 seconds or so; however, the "replace battery" light isn't on, nor is the "overload" light. Logging in with PowerChute shows nothing wrong.
The thing was provided to us by a telecom provider to protect their equipment, however, their policy is that they've given it to us, so they don't do anything to fix it. A tech I talked to suggested it might be that the battery is now three years old, so it is beeping to tell us to replace it , and suggested I log in and change that battery replacement date. However, that doesn't appear to work and since he's not an APC tech, I doubt that's true anyway. But none of the KB articles I read refer to this - a chirp like this is supposed to come with a "replace battery" light.
Any suggestions on what I should do next?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:45 AM . Last Modified: 2024-03-13 01:26 AM
is it four beeps every 30 seconds or definitely just a single beep?
what LEDs do you infact see illuminated on the front panel?
if available, it may be helpful to connect a serial cable to it with the powerchute monitoring software to see if it reports anything interesting through there but with a battery issue as you suggested, you should see a replace battery LED and that beep would be a "chirp" every five hours for a minute each time, NOT once every 30 seconds.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:45 AM . Last Modified: 2024-03-13 01:26 AM
is it four beeps every 30 seconds or definitely just a single beep?
what LEDs do you infact see illuminated on the front panel?
if available, it may be helpful to connect a serial cable to it with the powerchute monitoring software to see if it reports anything interesting through there but with a battery issue as you suggested, you should see a replace battery LED and that beep would be a "chirp" every five hours for a minute each time, NOT once every 30 seconds.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.