Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79259members
343896posts

SC-1500s last only three years?

Solved
RogerStrong_apc
Crewman
Crewman
0 Likes
6
209

SC-1500s last only three years?

This was originally posted on APC forums on 4/28/2010


We have two SC-1500s, installed at the same time three or four years ago.

The "replace battery" warning activated on one of them. We replaced the battery, and we get a "battery disconnected" warning.

Before we could solve that problem, the "replace battery" warning activated on the other UPS. This time we had our supplier install the new battery. Again, now we get a "battery disconnected" warning.

We've tried letting them charge - with the alarms sounding - for several days.

The supplier is telling us that both UPSs are broken, and they want to sell us new ones.

Is this normal? One battery, three years, and then you must replace the UPS?


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
209

Re: SC-1500s last only three years?

This reply was originally posted by Laurie on APC forums on 4/29/2010


Those units should work fine. The problem is the power that the UPS outputs when on battery - the SC models output a step-approximated sine wave and the SMT units produce a pure sine wave. So as long as they are sized properly, they should work just fine.

See Answer In Context

6 Replies 6
UPS_Tech_apc
Ensign
Ensign
0 Likes
0
209

Re: SC-1500s last only three years?

This was originally posted on APC forums on 4/29/2010


got it in a nutshell my friend. SC1500i will not run ML350 prioliant servers..

will kill them. APC do not recommend running the particular model on the SC1500I ever, also a knowledge base article floating around.

I suspect you would have had load issues, perhaps when bouncing back from automated batt tests or mains fail.

Recommend upgrading to SUA1500I.

UPS_Tech_apc
Ensign
Ensign
0 Likes
0
209

Re: SC-1500s last only three years?

This was originally posted on APC forums on 4/28/2010


may i ask what server or equipment type is powered off the UPS ?

Maybe Proliant ML350 range ?

RogerStrong_apc
Crewman
Crewman
0 Likes
0
209

Re: SC-1500s last only three years?

This was originally posted on APC forums on 4/29/2010


Both UPSs powered a Proliant ML350 each. (One with HP branding and the other older one with Compaq branding.)

I've unplugged both UPS's, and left them plugged in with and without a load for days, both turned on and off.

Thanks

BillP
Administrator Administrator
Administrator
0 Likes
0
209

Re: SC-1500s last only three years?

This reply was originally posted by Laurie on APC forums on 4/29/2010


Did you try a pull plug test at all to see if the unit actually functions when it's supposed to be running on battery?

RogerStrong_apc
Crewman
Crewman
0 Likes
0
209

Re: SC-1500s last only three years?

This was originally posted on APC forums on 4/29/2010


Thanks!

I couldn't find a knowledge base article on the APC site, but I found several forum threads on the HP site once I knew what to look for.

The vendor wants us to replace them with the SMT750, SMT1000 or SMT1500. I can't find any information to tell me whether this will give us the same problem as the SC models.

Any comments?

Thanks again.
- Roger Strong

BillP
Administrator Administrator
Administrator
0 Likes
0
210

Re: SC-1500s last only three years?

This reply was originally posted by Laurie on APC forums on 4/29/2010


Those units should work fine. The problem is the power that the UPS outputs when on battery - the SC models output a step-approximated sine wave and the SMT units produce a pure sine wave. So as long as they are sized properly, they should work just fine.