Restarting Servers when power is restored

This was originally posted on APC forums on 9/6/2016


"They are also set to then send a startup command to the servers once the UPS has been back on power for a certain time and has enough battery power to handle the whole load for enough time that they could shut down again if needed"

How would I go about configuring this? Is this something I would setup on our NMC? This response was posted by an anonymous source online. 


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
214

Re: Restarting Servers when power is restored

This reply was originally posted by Bill on APC forums on 9/7/2016


Hi,

For the servers to restart following a shutdown event you must configure the BIOS of the servers to restart when AC is restored. Since the servers are off there is no way for an application to command them on. To ensure that AC is cut to allow the server to power back up after a power failure you need to configure PowerChute Network Shutdown to shutdown the UPS. By doing so AC will be cut to the servers and when the BIOS see that AC has been restored the server will restart automatically. 

There is Knowledge Base document FA159550 on this subject and there have been quite a few discussions on this forum concerning this. The Knowledge Base document recommends setting the BIOS to last state however some people have recommend setting the BIOS to always on. I recommend setting the system to last state and if that is not compatible change to always on.

To configure a outlet group shutdown and power in the NMC go to Configuration - Outlet Groups (review the help files for assistance with the settings).  

See Answer In Context

Attachments
3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
214

Re: Restarting Servers when power is restored

This reply was originally posted by Bill on APC forums on 9/6/2016


Sam,

What model UPS are you asking about? Also, what is the model of the NMC and firmware? 

munroe7_apc
Crewman
Crewman
0 Likes
0
214

Re: Restarting Servers when power is restored

This was originally posted on APC forums on 9/6/2016


About UPS
 
Model: Smart-UPS SRT 3000
SKU: SRT3000RMXLT
Serial Number: AS1624390199
Firmware Revision: UPS 05.3 (ID1010)
Manufacture Date: 06/15/2016
 
Apparent Power Rating: 3000 VA
Real Power Rating: 2700 W
 
Battery SKU: APCRBC152
 
   
BillP
Administrator Administrator
Administrator
0 Likes
0
215

Re: Restarting Servers when power is restored

This reply was originally posted by Bill on APC forums on 9/7/2016


Hi,

For the servers to restart following a shutdown event you must configure the BIOS of the servers to restart when AC is restored. Since the servers are off there is no way for an application to command them on. To ensure that AC is cut to allow the server to power back up after a power failure you need to configure PowerChute Network Shutdown to shutdown the UPS. By doing so AC will be cut to the servers and when the BIOS see that AC has been restored the server will restart automatically. 

There is Knowledge Base document FA159550 on this subject and there have been quite a few discussions on this forum concerning this. The Knowledge Base document recommends setting the BIOS to last state however some people have recommend setting the BIOS to always on. I recommend setting the system to last state and if that is not compatible change to always on.

To configure a outlet group shutdown and power in the NMC go to Configuration - Outlet Groups (review the help files for assistance with the settings).  

Attachments